Maquis
Well-known member
I didn’t watch the video, but it sounds like it’s wrong. 8-3 Romex is only good for 40A (32A charge rate). If you are going to install 14-50 receptacles on 50A breakers, it’s not sufficient. You need either #6 Romex or #8 THHN in conduit. Putting Romex in conduit does not increase its ampacity.Got it. So did the guy in the youtube video I watch do it wrong by splicing the wires and not doing a subpanel with breakers? If I do this, can I then use 8/3 romex via conduit or do I still need separate wires for my new run to the 2nd charger?