I’m still wondering if the mobile charger requires the neutral for it to work.
At this point I’m inclined to spend the extra $$ for the 6/3 Romex and wire in a NEMA 14-50 outlet and then run 6/2 a couple of feet to hardwire in the ChargePoint.
If the mobile charger doesn’t require a neutral then it would be nice ifFord would offer a 6-50 plug as an alternative.
No, it does not use the neutral. The 14-50 is supplied on most EVSEs because they are so widely available at campgrounds.
The NEC does not allow more than one outlet on an EVSE circuit. Note that the NEC defines outlet as “the point where utilization equipment connects to premises wiring.” It’s not limited to receptacles.
In your case, you would have 2 outlets, the 14-50 and the hard-wired Chargepoint.
p52Ranch
Bryan
OK
I was considering installing a double pole double throw switch to isolate the EVSE circuit but those are about $500 for 60 amps. I also have considered installing a breaker box to segregate the 14-50 outlet from the ChargePoint wiring.
beatle
Springfield, VA
Sounds unnecessarily complex. I didn't catch what trim level you've ordered, but I assume it's not one with Ford's hardwired EVSE or I assume you'd just use that.
For mobile I don't plan to use the Ford one at all due to the plug limitation. I plan to use a Tesla UMC and a J1772 adapter. The Tesla UMC has many different plug adapters including the 6-50 and common dryer plugs like the 6-30 and 14-30.
Amps
Mid-Atlantic
Bolt
Wouldn't you then need to increase the size of the conductors feeding the new 'sub-panel'/breaker box?
Ford designed the mobile charger to use the optional 240v 50amp NEMA 14-50 outlet for various reasons - this is the outlet sizing that provides not only the 30amps of power, and more, but can be available for upgrading to higher amperage charging at a later date. Also, this is a very COMMON outlet at campgrounds, where it may be very convenient as an emergency charging option stop, if needed, or to simply provide 240v charging during your camping stay. On another note, the NEMA 14-50 is also much more common now for residential CLOTHES DRYERS and OVENS. The neutral is not always needed in every situation, no, but it is there for those devices and appliances that DO need it.
A Lightning EVSE mobile charger will not need the Neutral since both legs of power are drawing the exact same amount all the time.
A 50amp motorhome, though, does NOT draw the same amount of power on both legs, so the Neutral is required to 'balance' the load.
A new Clothes Dryer requires the Neutral for safety.
An OVEN or stove top requires the neutral.
As a last note: there are many and varied 50amp 'adapters' for different situations surrounding the use of a NEMA 14-50 outlet. It gives the user many options. Other 240v outlets that are not as common will not provide the Neutral and therefore not the options of the NEMA 14-50.
Nothing in the NEC would require that as long as the feeder has the correct over current protection.
Of course, only one of his circuits could be used at a time without tripping the breaker feeding the sub panel.