Sponsored

Ford Lightning with an onboard power system that provides a 240V output, tw0 110vac 180 degree?

Whammy Bar

Well-known member
Joined
May 30, 2022
Threads
22
Messages
543
Reaction score
831
Location
SoCal
Vehicles
1971 F100 + 2022⚡Lariat ER
Occupation
Electrician
Outside house solar controller and another panel

1736723859923-2a.jpg


1736723983473-0t.jpg


Solar controller, input maximums 500DC. output 220vac ( European standard. ) 60HZ. couldn't separator two 110vac.
So much dodgy looking shit in a single blurry photo.

God speed OP.
 

Effonefiddy Lightning

Well-known member
First Name
Alfred
Joined
Jun 2, 2022
Threads
2
Messages
267
Reaction score
209
Location
California
Vehicles
23 F150 Lightning SR Antimatter Blue /2023 Model Y
Occupation
Retired
If your transfer switch also transfers the neutral, then there is no need.

If your transfer switch does not transfer the neutral, then you have the usual problem with the GFCI tripping. Lifting the ground on the house end of the cable at the generator inlet receptacle creates no danger or safety hazard. None. Zero. The only hazard is the code Nazis trying to throw books at you. Every circuit breaker, GFCI, AFCI, and other existing protection devices will all still work. There is no lost or disabled functionality that existed in the normal power configuration. The ground wire in your generator cable is intact and protecting the cable itself. Like if someone ran it over with a lawn mower or water got in it.

It doesn't meet perfect code requirements. But this is temporary, safe, emergency power.
Thank you so much for the advice.
 
 