Instead of stressing over the delivery and installation of the FCSP after I get the Lightning, I intend to install the ChargePoint Home Flex CPH50 in a secondary location. Later I will have an electrician install the FCSP in the primary location, in preparation for a future install of the HIS.
As a hardwired CPH50 requires 90c rated install for 50A charging, does anyone know if I can oversize the panel and breaker if they are rated at 75c? I plan to use 90c rated THHN 6g wire, a 70a (BR270) breaker, and a 125amp Eaton panel.
As a hardwired CPH50 requires 90c rated install for 50A charging, does anyone know if I can oversize the panel and breaker if they are rated at 75c? I plan to use 90c rated THHN 6g wire, a 70a (BR270) breaker, and a 125amp Eaton panel.