That's a common misconception. The screen display is showing average over many mains cycles. The actual instantaneous reverse power can be up to many kW's (e.g. when a large load like electric heater, microwave or dryer turns off) for a short time before the export limiting kicks in within 2s (UL standards requirement). Export limiting is fine for meeting interconnection metering requirements but much too slow to prevent tripping protection shutoff.One thing I do remember on the Sol-Ark, is you can add in a buffer of grid power to avoid sending in a reversal of power back to the grid. I keep mine at zero, which means you can see on my screen that when a load turns off, sometimes the grid will pick up a few watts. But if you are always importing a few watts from the grid, this might provide a buffer for any sudden reversal. I wonder if it would work in this scenario.