Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps (edit…20amps). I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
Sponsored

 
Last edited:

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
185
Messages
13,769
Reaction score
14,804
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps. I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
The ground was not used?
Only the two HOTs were connected?
 

Whammy Bar

Well-known member
Joined
May 30, 2022
Threads
23
Messages
610
Reaction score
941
Location
SoCal
Vehicles
Reliable - 1971 F100; Unreliable - 2022⚡Lariat ER
Occupation
Electrician
Update on my overheating receptacle issue.
I opened up the outlet and I can’t tell exactly which size the THHN is, however it is solid copper and it’s either 12 or 10ga, so big enough for 30amps. I tightened down the lugs. They were reasonably tight, but I really cranked them down. It was still warm. I basically determined this is likely an issue with the EVSE so I started troubleshooting it.
I opened up the EVSA itself with a plan to replace the wall side plug. It’s an early generation Lectron charger. What I found is disappointing. Although it’s a four wire (three conductor) plug (NEMA 14-30)…only 2 conductors are being utilized. Which I would imagine is what’s causing the heat. I’ll be finding a different EVSE.
Conductors need to be sized for continuous load. So if you're rocking yellow romex (12ga) your limits 16A. If you have the Halloween orange (10ga) then your limited to 24A.
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
185
Messages
13,769
Reaction score
14,804
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired

Sponsored

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
185
Messages
13,769
Reaction score
14,804
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER & 2024 HD Road Glide CVO-ST
Occupation
Retired
Sorry, I'm confused................. two discussion on this thread.
 

DiveMan911

Well-known member
First Name
R.J.
Joined
Feb 24, 2022
Threads
6
Messages
166
Reaction score
186
Location
Maui, HI
Vehicles
'06 Acura TL, '13 Ford Escape
Occupation
Flight Nurse
Conductors need to be sized for continuous load. So if you're rocking yellow romex (12ga) your limits 16A. If you have the Halloween orange (10ga) then your limited to 24A.
It’s not Romex, it’s THHN in conduit. Conductors are wrapped in electrical tape identifying them, so I can’t read their size. I also don’t have a guage tool, so I was eyeballing it. Basically, an exact science. It’s definitely big enough for a 20 amp breaker, just seems silly they did a 20amp breaker on a 30amp receptacle.
 
 