Best home charger CANADA.
Kev12345
Ram 1500
in Canada go hardwired. you'll pay a bit more for a hardwired charger but...
- slightly faster charging 48amps vs 40amps
- install cost will be cheaper. 50amp plugs need a neutral (3 wire), hardwired only requires 2.
- 50 amp outlets require GFCI breakers by code which are expensive and can nuisance trip. hardwired units are ok with regular cheaper breakers.
topofsuperior
steve
2023 lightning Lariat
Unless you really need the 48 amps stick with the 40 amp chargers - 48/60s need to be hardwired - mention hardwiring and EV charger to an Electrician and that’s like blood in the water for a shark. A lot of jurisdictions have extra hoops/code/permit requirements for “EV Chargers” that just means you get to pay more.
A 14-50 is just a “plug” - generic code rules/permits/costs. Your EV Charger is just something you plug into it.
And in future if the EV charger fails, toss/return/plug in a new one - no electrician needed.
I am with you on this. I was able to DIY and even with the permit was a fraction of what the hard wired chargers are listed for.
Kev12345
Ram 1500
not sure what the requirements are in the US but in Canada the installation will always be cheaper with a hardwired charger. Mainly because of the GFCI breaker requirement for the plug which can reach above $300cad.
*edit - GFCI breakers only required with outdoor installations in Canada. CEC 86-306
Ford F-150 Lightning Best home charger CANADA. IMG_1706
Ford F-150 Lightning Best home charger CANADA. IMG_1705
earlyadopt
Woodstock
MachE, Lightning XLT
Insurance Broker
Hi there. Im
New to the site and we’re very close to pulling the trigger on a 24 lariat. Just wondering what would be my best and most economical option for home charging….. I don’t think I want to shell out nearly $2000 CAD for the for pro charger…… I will need to have a 240 installed in my garage so would a “plug and play unit” be best, or have it hardwired ? Thanks for the help (not the best navigator on forums)
I strongly suggest the Tesla Universal Wall Connector. This unit future proofs you. NACS is the standard adapter now. This unit has both J1777 and NACS. never worry about having the wrong connector down the road. Your Tesla buddies will appreciate it as well.
Adventureboy
I've had the Grizzl-e 40 Amp smart charger - it was troublesome and I use it now at my parents in dumb mode at 40 amps - it has been good that way but not flexible.
I have a 48 amp Emporia at home and it is a much more flexible charger for tracking and adjusting. It is hard-wired and 48 amps on a 60 amp breaker gets me out of a pinch when I come home late low on power. I normally charge at 32 amps to cover my daily use and the Emporia is really easy to adjust through the app as needed. To me, it was well worth the upgrade.
topofsuperior
steve
I just did an install of a 50 amp outlet in Ontario Canada with an ESA inspection. Did not require the gfci.
Kev12345
Ram 1500
Maybe you got lucky with the inspector? It's clearly stated in the NEC. section 625.54
  • GFCI protection for all single-phase EV charging outlets that are 150 volts to ground or less and 50 amperes or less
  • GFCI protection for all EV charging outlets, regardless of location
topofsuperior
steve
Maybe you got lucky with the inspector? It's clearly stated in the CEC. section 625.54
I had both the experienced supervisor and then a newbie inspector for some other deficiencies on my project. I forgot to put paste on the aluminum wire so I had an experienced electrician walk me through to get it done right.
Kev12345
Ram 1500
Sorry guys, I was mistaken when it comes to EV charging section 86 of the Canadian Electrical Code. GFCI protection is ONLY required when installed outdoors.
I guess indoor GFCI protection is America only. My bad!