Maquis
Well-known member
It’s called a spider box.You're right. I missed the "of 120V" in the original claim.
That said, drawing 30A per phase via the 5-20R outlets which are clearly marked as 20A max is a bad idea (and I am surprised Ford's design doesn't use a separate breaker to prevent this). Even if the wiring from inverter to each outlet is appropriately sized (10ga per the small conductor rule if NEC applies, which I suppose it may not) and the outlets themselves are rated for use at 75C (questionable) nothing you can plug into them is going to be sized or rated to carry 30A of current. And you'll need to build a very dangerous extension cord with a 20A plug on one end and 30A receptable on the other end - or overload a nominally 20A power strip, the internal wiring of which will not be designed or rated for a 30A load.
If you want 30A per phase of 120 to run exclusively 120V devices, one of the power strips/breakout boxes used in datacenters for exactly this purpose (they even have the correct locking 30A connector on the upstream end) would work, but they're not weatherproof. Maybe with the prevalence of TT-30 in the RV world, there is something similar and weatherproof available there? In any case, if you want 7kW of power for 120V devices, better get it from the 30A receptacle, not the 20A ones.