I talked to a Ford rep at the San Antonio event last week. They had a video showing conduit connecting to the CSP. It looked like 3/4” and with two conduits (one for A/C “in” and the other for DC “our” for the HIS) connected via knock-outs on either lower side of CSP.
Question: Did they show anyone it actually working to charge or function like the HIS is suposed to? I ask this as there is no video out there of the system actually performing as functioned? or a demo of it, right? If thats the case, maybe the conduit was just for show...
Sponsored

 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,664
Reaction score
4,674
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Thanks! That confirms my thoughts, and my contractors advice, to have a separate conduit for the DC return. Do you have any sources that could advise the required conductor size for the DC?
We really need to see the specs, but 9.6 KW at 400 VDC equates to 23 A. But since the 9.6 should be the delivered AC, inverter losses means it will be a bit more than that…maybe another 10% or so.

Correction: Specs for the HIS state that an EV voltage as low as 290 is acceptable. That makes the maximum current about 36 A DC. #8 copper wire would then be the minimum size.
 
Last edited:

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
999
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
We really need to see the specs, but 9.6 KW at 400 VDC equates to 23 A. But since the 9.6 should be the delivered AC, inverter losses means it will be a bit more than that…maybe another 10% or so.

I got nowhere getting any HIS-related install info with SunRun, so this afternoon I called the manufacturer Delta directly…they were very helpful. The support person I talked to confirmed the need for two #8 conductors on the DC return from the EVSE (Charge Station Pro)…finally, an answer! The rep from Delta encouraged that self-installers and installing contractors contact them directly with any technical and/or installation questions.

From their BDI Technical Sheet:

Delta Electronics (Americas), Ltd.
46101 Fremont Blvd, Fremont, CA 94538

Sales Email: [email protected]
Support Email: [email protected]
Sales Hotline: +1-877-440-5851 or +1-626-369-8021
Support Hotline: +1-877-442-4832
Support (Intl.): +1-626-369-8019
Monday to Friday from 6am to 6pm PST (apart from Holidays)

www.Delta-Americas.com
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
53
Messages
688
Reaction score
477
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
I agree it initially will, but upon future upgrade to the HIS, I do believe the AC conductors would be relocated from the House Panel to the HIS since the HIS contains the Automatic Transfer Switch.
I assumed both came from the HIS per teh lightwieght schematic from Delta. What would be great is if it passed DC from solar panels to the truck directly...
 

adoublee

Well-known member
Joined
Aug 30, 2021
Threads
12
Messages
749
Reaction score
689
Location
Midwest
Vehicles
2 EVs
I got nowhere getting any HIS-related install info with SunRun, so this afternoon I called the manufacturer Delta directly…they were very helpful. The support person I talked to confirmed the need for two #8 conductors on the DC return from the EVSE (Charge Station Pro)…finally, an answer! The rep from Delta encouraged that self-installers and installing contractors contact them directly with any technical and/or installation questions.

From their BDI Technical Sheet:

Delta Electronics (Americas), Ltd.
46101 Fremont Blvd, Fremont, CA 94538

Sales Email: [email protected]
Support Email: [email protected]
Sales Hotline: +1-877-440-5851 or +1-626-369-8021
Support Hotline: +1-877-442-4832
Support (Intl.): +1-626-369-8019
Monday to Friday from 6am to 6pm PST (apart from Holidays)

www.Delta-Americas.com
How about help with direct and timely purchase of the HIS?
 

Sponsored

adoublee

Well-known member
Joined
Aug 30, 2021
Threads
12
Messages
749
Reaction score
689
Location
Midwest
Vehicles
2 EVs
I assumed both came from the HIS per teh lightwieght schematic from Delta. What would be great is if it passed DC from solar panels to the truck directly...
It can, via a couple DC-DC converters to match the solar maximum power point voltage to the EV charging voltage. Assuming it is not locked out by software that is.
 

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
999
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
How about help with direct and timely purchase of the HIS?
I expect that will need to be a conversation between Ford and it’s partner SunRun about how Ford would like it’s customers that live outside SunRun’s service area treated🤔. We all should be on an equal footing….and, expect Ford is the only one that could influence SunRun to do that……
 
Last edited:

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,664
Reaction score
4,674
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
I got nowhere getting any HIS-related install info with SunRun, so this afternoon I called the manufacturer Delta directly…they were very helpful. The support person I talked to confirmed the need for two #8 conductors on the DC return from the EVSE (Charge Station Pro)…finally, an answer! The rep from Delta encouraged that self-installers and installing contractors contact them directly with any technical and/or installation questions.

From their BDI Technical Sheet:

Delta Electronics (Americas), Ltd.
46101 Fremont Blvd, Fremont, CA 94538

Sales Email: [email protected]
Support Email: [email protected]
Sales Hotline: +1-877-440-5851 or +1-626-369-8021
Support Hotline: +1-877-442-4832
Support (Intl.): +1-626-369-8019
Monday to Friday from 6am to 6pm PST (apart from Holidays)

www.Delta-Americas.com
Thanks…I corrected my post #92 with additional information.
 

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
999
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
Thanks…I corrected my post #92 with additional information.
Welcome…the Support Rep also said the Amps on the DC side was 36.7 in his book…

.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,664
Reaction score
4,674
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Welcome…the Support Rep also said the Amps on the DC side was 36.7 in his book…

.
👍🏼

While it’s almost impossible for the current to be that high with the Lightning’s 400V architecture, the wiring needs to be capable of worst-case.
 

Sponsored

F150LER

Well-known member
Joined
Apr 21, 2022
Threads
2
Messages
89
Reaction score
66
Location
Us
Vehicles
F150L
If I do a small solar install, do I need an another in inverter or will the HIS handle that?
 

adoublee

Well-known member
Joined
Aug 30, 2021
Threads
12
Messages
749
Reaction score
689
Location
Midwest
Vehicles
2 EVs
If I do a small solar install, do I need an another in inverter or will the HIS handle that?
How small? You want at least 4-5 panels to build enough voltage for the solar input start-up. From there you need to use APS or Toigo devices for rapid shutdown to isolate voltage at panels. This apparently requires a rapid shutdown transmitter option be bought with HIS inverter. With all that, yes it is a solar inverter.
 

F150LER

Well-known member
Joined
Apr 21, 2022
Threads
2
Messages
89
Reaction score
66
Location
Us
Vehicles
F150L
How small? You want at least 4-5 panels to build enough voltage for the solar input start-up. From there you need to use APS or Toigo devices for rapid shutdown to isolate voltage at panels. This apparently requires a rapid shutdown transmitter option be bought with HIS inverter. With all that, yes it is a solar inverter.
Got it. How big could I go on the HIS? I want to go Solar so trying to figure out if this makes sense if you also use it as Solar inverter.
 

adoublee

Well-known member
Joined
Aug 30, 2021
Threads
12
Messages
749
Reaction score
689
Location
Midwest
Vehicles
2 EVs
Got it. How big could I go on the HIS? I want to go Solar so trying to figure out if this makes sense if you also use it as Solar inverter.
Rule of thumb might be 12kW of panels based on 125% of inverter ability to convert 9.6kW to AC for home/grid. You might reasonably go up from that if a connected battery is available to charge during the day. Going up you would need to respect rules of up to 4x12A of input current, cold weather adjusted cap of 480V per string. That adds up to just over a theoretical 23kW of actual solar power (no other solar input power cap listed) but you will never get up that high on voltage and get that exact peak current. It is essentially 4 strings of panels, with max number of panels you can include dependant on panel details and how cold your location gets.
 

blpublic

Well-known member
First Name
Brian
Joined
Nov 18, 2021
Threads
3
Messages
55
Reaction score
58
Location
Missouri
Vehicles
2016 F150 XLT
Question: Did they show anyone it actually working to charge or function like the HIS is suposed to? I ask this as there is no video out there of the system actually performing as functioned? or a demo of it, right? If thats the case, maybe the conduit was just for show...
You could not tell from the video if it was real, and the dummy unit in San Antonio was not functional.