Great write up. I was tempted to do this, but I didnāt understand a couple details well enough to make sure I wasnāt posting something half-assed.it should be noted that the HIS can be installed without solar - you're not required to use the solar string inputs. Is the cost high? Perhaps slightly, but this is early adopter territory. 10kW string inverters typically run low-to-mid $2,000s for cost today (maybe a bit less expensive for the big big guys). Add the other components (battery & grid disconnect switch), profit, and early adopter tax and it seems about right.
Personally, I'd think Enphase has to do more development work than all the other string inverter manufacturers (Delta, SMA, SolarEdge, etc.) because their inverters are all 25-50V, ~250-350W and they'd be designing a new "big" inverter. The existing string inverter manufacturers just have to get the software right to create the microgrid (instead of just shutting down due to UL1741).
Here's what needs to happen to supply backup power from the system when failure is detected. It's more complex than the typical UL1741 grid-tie solar install:
* Something needs to become aware of the grid failure (MID, above)
* Grid must be immediately disconnected (but still monitored for return) (MID)
* Inverter uses its dark-start battery to establish the power baseline for a microgrid, keeping the system alive to continue all the rest of the steps to get the truck's power online (inverter using dark-start battery)
* Truck must be instructed to wake up, turn on the HV contactors, and supply the battery to the CCS DC terminals if no errors (EVSE)
* Inverter then begins using DC power available from the truck to supply loads from the home and adjusts to maintain proper voltage while monitoring for ground faults (truck must immediately disconnect DC terminals if DC ground fault detected, which is why EVSE plays a role here)
* When grid power return is detected, the grid can be reconnected to the system by the MID and the inverter can begin tapering its supply and disconnects the DC when no longer needed
* Truck recharges via EVSE
As you can see, it's not just as simple as a cheap 400 VDC inverter.
All the other solar PV that's connected (whether Enphase microgrid or some other external system) will use UL1741 to integrate and will work to match frequency and regulate voltage based on load.
One question I have is: Does the EVSE actually switch the DC, or does it just tell the truck to open/close the HVB contactor? I would think the latter, but Iām interested in your opinion and reasoning. Thanks!