So it seems to that it comes down to the "Exception" and if the inspector deems the home owner "qualified". IMHO (take that with a grain of salt) the lockout is what makes the end user " qualified" ... why else would it be installed? BTW, thank you for the explanationThe hair dryer thing would cause a short and pop a breaker for the circuit it is on.
Wiring a sub-panel in an out-building is equivalent to what you should be doing through the transfer switch, where the "out building sub-panel" is your circuits in the transfer switch being powered in the house by the Lightning. The neutrals should not be grounded in the sub-panel since they are already grounded at the main panel, in your case, the Lightning, but you still want to have a continuous ground between the Lightning and the sub-panel.
The above illustrates this.
The sub-panel circuits have their neutrals going to the neutral terminals on the neutral bar (right side of sub-panel) but the sub-panel neutral bar is NOT ground at the sub-panel.
Unfortunately many licensed electricians may not be familiar with wiring a generator to a dwelling through a transfer switch, and will not do it correctly. But if they understand it as being like wiring a sub-panel, then they should get it.
A lock-out kit might not be deemed code compliant - it depends.
Your locality may allow it under the exception of NEC 702.5, but the issue is whether it is accessible "only" by "qualified persons."
-----
702.5 Interconnection or Transfer Equipment
(A) General
Interconnection or transfer equipment shall be required for all standby systems subject to the requirements of this article. Equipment shall be suitable for the intended use and shall be listed, designed, and installed so as to prevent the inadvertent interconnection of all sources of supply in any operation of the equipment. [e.g., a Transfer switch]
Exception: Temporary connection of a portable generator without transfer equipment shall be permitted where conditions of maintenance and supervision ensure that only qualified persons service the installation and where the normal supply is physically isolated by a lockable disconnecting means or by disconnection of the normal supply conductors.
-----
702.11 Portable Generator Grounding
(A) Separately Derived System
Where a portable optional standby source is used as a separately derived system, it shall be grounded to a grounding electrode in accordance with 250.30.
-----
250.30 (A) Grounded Systems
A separately derived ac system that is grounded shall comply with 250.30(A)(1) through (A)(8). Except as otherwise permitted in this article, a grounded conductor shall not be connected to normally non-current-carrying metal parts of equipment, be connected to equipment grounding conductors, or be reconnected to ground on the load side of the system bonding jumper.
-----
Translation:
The neutral is a grounded conductor.
The dwelling circuits are the load.
The neutral (grounded conductor) shall not be (also) connected to ground at the load.
-----
Separately Derived System. An electrical power supply output, other than a service, having no direct connection(s) to circuit conductors of any other electrical source other than those established by grounding and bonding connections. (CMP—5)