OK, I have a meter pole that has a meter and a great big 200A disconnect that services the entire property.
I want to pull a 100A rated set of wires off the protected (downstream) side of the 200A breaker, and run them about 18" to a 100A breaker box. From which I will then move on with an EVSE install (Intend to try the Ford unit initially.
The 100A sub breaker will be attached via rigid metal conduit, about 4" from the main box. I think this is code. Since the distance is so short. Technically, the short run of 100A rated wire is "unprotected" since it is attached to a 200A breaker. But I think I read somewhere that with that short a run, in metal conduit, it can be done, so long as it of course terminates at an appropriately sized breaker.
Interestingly the PO wired a whole garage off the 200A breaker, ran wires underground for like 20 feet, and then put a 20A breaker in the garage. I suspect that is NOT code, or entirely bright honestly. But that's not my problem today. Its not the garage that is at risk, but if someone decides to dig a post hole and hits that line, they would get all 200A until something burned clean through........
I want to pull a 100A rated set of wires off the protected (downstream) side of the 200A breaker, and run them about 18" to a 100A breaker box. From which I will then move on with an EVSE install (Intend to try the Ford unit initially.
The 100A sub breaker will be attached via rigid metal conduit, about 4" from the main box. I think this is code. Since the distance is so short. Technically, the short run of 100A rated wire is "unprotected" since it is attached to a 200A breaker. But I think I read somewhere that with that short a run, in metal conduit, it can be done, so long as it of course terminates at an appropriately sized breaker.
Interestingly the PO wired a whole garage off the 200A breaker, ran wires underground for like 20 feet, and then put a 20A breaker in the garage. I suspect that is NOT code, or entirely bright honestly. But that's not my problem today. Its not the garage that is at risk, but if someone decides to dig a post hole and hits that line, they would get all 200A until something burned clean through........