Well pump tripping GFCI

admo

Member
Joined
Nov 18, 2024
Threads
2
Messages
6
Reaction score
5
Vehicles
f150 lightning
Hello everyone, I have setup truck as generator (240v to generator port) for my home fine. I have a neutral switching transfer switch and can power lights and refrigerators and freezers fine (the open neutral issue is solved). My issue is a GFCI fault (as reported by the truck display) from my well pump immediately when it starts. The well pump is on a 30amp breaker and draws under 15 amps when running, but it's startup/inrush is ~34 amps. My initial thought was "well that's the problem" but my house 30amp breaker is not tripping for this well pump on grid power, additionally I'm seeing some large capacitors in the control box for the pump which I believe is to handle this inrush issue.

The core question I'm trying to solve before spending a lot of money is: my truck is displaying a GFCI fault message. I had thought the GFCI message in the truck was indicating a general breaker issue but doing more reading on these forums I'm seeing other people saying there is also an "overload" message. Does anyone know more detail on this and what specifically either message means?

I read some people use soft starters to smooth out motors with large inrush current issues but the well pump companies here don't know or don't want to talk about them. On the other hand the well pump is 30 years old and I presume out of spec if it is on a 30 amp breaker and can draw more than 30 amps. So I am trying to find ways to figure out if the issue is the inrush current or a true GFCI fault. A well pump with any shorts in its wire or housing would of course trip GFCI leading to me needing to replace the pump, while the in rush issue I might be able to solve with a soft starter but they also have some expense.

I don't have details on the well pump unfortunately, only that it was placed 360 feet down. Some internet reading suggests GFCI faults could also occur from extremely long wire runs but I don't know if 720 feet is considered "extremely long". I do have the full four wires running down the well.

Thank you to anyone who has tips, I have not been able to convince the electrician or well pump company to use their expertise to figure it out. I'm also a bit naive on electrical stuff so I wanted to be really sure before I take a crack at installing a soft starter.
Sponsored

 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,417
Reaction score
4,292
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER

Ricks Lightning

Well-known member
First Name
Rick
Joined
Jun 13, 2024
Threads
6
Messages
143
Reaction score
108
Location
Los Angeles
Vehicles
2023 F150 Lightning Pro, 2024 F150 Lightning Flash
Occupation
Plumbing Contractor
I'm not an expert in well pumps, but am in sump pumps, ejector pumps, circulating pumps. The last thing you want on a pump is a gfci breaker. same with a fridge unless you want spoiled food. 30 year old pump is most likely the issue as the same think happens with submersible pumps that sit in the water for a long time.

Rick
 

Firn

Well-known member
Joined
Aug 26, 2024
Threads
9
Messages
228
Reaction score
206
Location
USA
Vehicles
23 Pro ER
Traditional house breakers don't trip immediately, which is why they can handle an inrush of 34 amps. The lightning on the other hand will immediately trip.

Soft starts are just for this purpose. It's not traditional for a well pump, which why the well guys don't know about it, but it's pretty common for HVAC systems so go talk to an HVAC guy.

In the end it think a soft start is just what you need.
 
OP
OP

admo

Member
Joined
Nov 18, 2024
Threads
2
Messages
6
Reaction score
5
Vehicles
f150 lightning
Firn's advice differs from Maquis' and returns back to the thought I had that there are different error messages from the Lightning when it disconnects the Pro Power. I am seeing a GFCI message but Firn you suggest something that I believe would be an overload message. If the GFCI message indicates a GFCI fault then a soft starter seems like it would not solve the problem.

This post on these forums triggered my wondering on this, I didn't realize there were two different error messages: https://www.f150lightningforum.com/...er-breaker-with-120v-welder.18452/post-370924
 

Sponsored
OP
OP

admo

Member
Joined
Nov 18, 2024
Threads
2
Messages
6
Reaction score
5
Vehicles
f150 lightning
Thank you both Maquis and Rick, for the information. I am reading up to figure out this isolation transformer thing. Part of the difficulty here is that I have no method to test and confirm either hypothesis (GFCI fault via short versus overloading the circuit) aside from the error message from the truck. I don't believe my multi-meter would show the kind of voltage drop that would trigger the GFCI (Also I hope I said these electrical things correctly).

Although If there is a nicer multi-meter out there that does show this kind of precision that would be cheaper than guessing and installing either solution.
 

shelnian

Well-known member
First Name
Ian
Joined
Sep 15, 2022
Threads
0
Messages
48
Reaction score
23
Location
Seattle
Vehicles
2022 Mach-E Premium ER, 2023 Lightning XLT SR 312A
Occupation
Retired
If you try to draw more than 7200 watts, pro-power cuts out and indicates you are drawing more power than it's rated for. You have to reduce the load and then hit the reset button on the Sync screen.
 

hturnerfamily

Well-known member
First Name
William
Joined
Jan 8, 2022
Threads
45
Messages
1,872
Reaction score
2,240
Location
rural Georgia
Vehicles
22 LIGHTNING PRO IcedBlueSilver 8/23/2022
Occupation
Owner
it can be somewhat aggravating and annoying when ProPower 'works', then cuts out right when you least expect it

- home-based breakers do NOT work the same exact way that our electronic-based circuits work within the LIGHTNING's ProPower. Regular breakers are based on 'heat', whereas electronic circuits are MUCH MORE EXACT... when they read 30+amps, they IMMEDIATELY trip. An 'in rush' when a compressor or similar motor starts up is problematic.

- the truck's circuitry can seem to be bypassed when it comes to the sensitivity of the GFCI 'issue', at least until you add a substantial LOAD. It seems the additional amperage tips the scales toward tripping.*

*one example: my camper.
Our previous campers we towed had no issues using ProPower, while towing or hooked up to the truck, even the air conditioner or microwave.
Interestingly, though, our newest camper, very similar to the previous two, will NOT work readily with ProPower, meaning that the truck's power shuts off immediately when plugging in the camper, while towing or hooked up to the truck.**
**The 'while towing', and/or 'hooked up to the truck', is ultimately the problem.
We all know the issue of the 'ground' wire. That connection was removed.
We all may also know the issue of the truck's GFCI not pairing well with other GFCI outlets, such as the one in my camper. I removed the GFCI outlet in favor of a 'regular' outlet.
These two changes created a solution, at least initially.

When I am NOT attached to the camper, my truck's ProPower can easily provide all the power I need, for EVERYTHING, and all at the Same Time. Sweet. It works the way it's supposed to.

When I AM attached to the camper, whether just the coupler on the ball, or the 7-pin 12v connector to the camper, if the breaker to the camper's 12v Converter is left ON, ProPower trips.
If, tho, I turn OFF this converter breaker, I can then use 'some' electricity in the camper...
when I turn on the microwave, or the air conditioner, though... bamm - I lose power, again.
It must be some type of 'grounding' issue with the camper, or it's Main Panel wiring, or, as I've surmised, the 12v CONVERTER wiring for the camper, to the camper's two batteries.

so, yes, it's aggravating, and maybe there is an ultimate solution, but, for now, I just use 'some' electricity, and if I need more, I completely unhook the camper from the truck, and everything works perfectly : )
Sponsored

 
 





Top