Indeed but this number ignores the time, either your own experienced time or an expensive electrician, to route circuits from the main breaker to the transfer switch breaker. I had thought the isolation transformer was a good solution, if it does whole house, because it would skip that re-wiring and be cheaper than more expensive transfer switch after you added man-hours.

But all of this is moot for me, I already have the transfer switch, yet it doesn't handle the pump, so I shall get the transformer installed and be happy with everything working.

I think my electrician was a little scared of this new idea and went a little overboard on the hardware but it worked out in the end (minus the well pump).
It looks like a 240VAC 30A transformer (7.2kVA) would cost in the neighborhood of $1700 and up, and would have to be wired to the house as well.

Wiring a transfer switch like the GENERAC 6853 should not cost too much.

Yes, it looks like you have a big Seimens disconnect/transfer switch and a whole separate breaker box too. Definitely on the expensive side compared to a GENERAC 6853 install.

Although the GENERAC manual is a bit obtusely written, basically the wiring is take the hots and neutrals from the circuits you want to back up and connect them to the corresponding hots and neutral prewired in the transfer switch. You also install a 50A breaker in your main service panel and power to the transfer switch when the utility is on (to power the backed up circuits from the utility).
Sponsored

 

Attachments

OP
OP

admo

Member
Joined
Nov 18, 2024
Threads
2
Messages
21
Reaction score
13
Vehicles
f150 lightning
It looks like a 240VAC 30A transformer (7.2kVA) would cost in the neighborhood of $1700 and up, and would have to be wired to the house as well.

Wiring a transfer switch like the GENERAC 6853 should not cost too much.

Yes, it looks like you have a big Seimens disconnect/transfer switch and a whole separate breaker box too. Definitely on the expensive side compared to a GENERAC 6853 install.

Although the GENERAC manual is a bit obtusely written, basically the wiring is take the hots and neutrals from the circuits you want to back up and connect them to the corresponding hots and neutral prewired in the transfer switch. You also install a 50A breaker in your main service panel and power to the transfer switch when the utility is on (to power the backed up circuits from the utility).
I still think the isolation transformer would be cheaper. You left out all the breakers you must buy and add to the Generac box, I thought those are like $50 each. Plus that time fishing wire around breaker boxes is not free. The isolation transformer Maquis linked was $700 and I presume the install is much simpler as well as implicitly power the whole panel.

The only downside I'm seeing to the isolation transformer is the power loss people talk about but I have no idea what that loss is in practice.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,445
Reaction score
4,337
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
I still think the isolation transformer would be cheaper. You left out all the breakers you must buy and add to the Generac box, I thought those are like $50 each. Plus that time fishing wire around breaker boxes is not free. The isolation transformer Maquis linked was $700 and I presume the install is much simpler as well as implicitly power the whole panel.

The only downside I'm seeing to the isolation transformer is the power loss people talk about but I have no idea what that loss is in practice.
Typical operating losses are 3 to 5% for small dry type transformers. Look for an efficiency curve or data sheet before you purchase. Your electrician can help interpret the data.