@chl I followed what you said here, and thanks for the great write up. I already purchased a Generac 6853 since that seemed to be the hot product. However, I have not opened it yet as I am still waiting on the FCPS and installation. Some people seem have it working by making sure the plug inlet and switch are not bonded. Do you think this is the wrong product and a GFI specific transfer switch is better?I believe you need a GFI transfer switch to avoid the ground fault tripping in the F-150 Lightning 240v/30A outlets which apparently are GFCI protected.
Most GFCI's found on portable generators are there to protect the 15/20A, 120-volt outlets, and not the 120/240 outlets that are used to connect to home transfer switches.
However, you need a GFI transfer switch to connect any generator (like to F-150 Lightning) to your home if the generator 120/240-volt outlets are GFCI protected - without a GFI transfer switch it creates a ground loop and trips the circuit.
I would have the same issue in my home I believe because I do not think my manual transfer switch that I use for my gas generator (use rarely) is a GFI transfer switch.
For the source of this info, see: https://www.electricgeneratorsdirec...ipping-a-Generator-With-a-Bonded-Neutral.html
I believe they are who I bought my equipment from years ago.
An example of a GFI transfer switch: https://www.wincogenerator.com/product/reliance-manual-transfer-switch/
Thanks!