Long story short (pun intended), the GFCI on the truck will trip off if the receptical ground wire is connected to the ground wire coming from the panel. So run all 4 wires from the panel to the generator plug and don't connect the green and connect the green from the truck side of the plug to the front of the plug and to the receptical hosing.
Because the generator (truck) is not connected permanently (ie for emegency use), it's legal (in a lot of states) for the ground to float.
One NOTE, I have one more thing to do before we call the inspector but the work was done with a permit and by a licensed electrician.
Because the generator (truck) is not connected permanently (ie for emegency use), it's legal (in a lot of states) for the ground to float.
One NOTE, I have one more thing to do before we call the inspector but the work was done with a permit and by a licensed electrician.