Has anyone used Pro Power OnBoard with an autotransformer to work around the bonded neutral issue?

I see reports of success with neutral transfer switches but I have used autotransformer with bonded neutral generators in the past and wondered if the same can be done with Pro Power OnBoard. Autotransformer has the added benefit of automatic load balancing between the 120V legs.
Sponsored

 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,393
Reaction score
4,247
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Do you mean isolation transformer? I can’t visualize how an autotransformer would work here.
 
OP
OP

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
152
Reaction score
66
Location
USA
Vehicles
Tesla Model 3
No. I mean autotransformer or perhaps more accurately neutral forming autotransformer. Specifically, only connecting the L1 and L2 from a 240V power source (e.g. generator) and connect L1, L2 and neutral without ground bonding from the autotransformer to loads.
 
Last edited:

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
169
Messages
12,165
Reaction score
12,810
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow & 2024 Harley-Davidson Road Glide CVO-ST
Occupation
Retired

Fastnf

Well-known member
Joined
May 21, 2021
Threads
2
Messages
117
Reaction score
177
Location
CALIFORNIA
Vehicles
2023 F150 lightning
Enphase uses a neutral forming transformer in their smart switch. Both their back up batteries and the input from solar are 240 volt with no neutral. I haven’t tried it but it would seem like you could connect pro power in the same manner. I am a month or so from getting my Enphase system operational. Once’s it up and running I will be looking at options to use pro power to charge the Enphase batteries during extended outages with low solar input (ie snow storms).
 

Sponsored

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,393
Reaction score
4,247
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Some thing like this?

Autotransformer-with-Generator.png


https://shop.pkys.com/autotransformer.html

I looked up via google for single phase 7.5 KW versions, kind of pricey 1500 to 3000 bucks!!
The problem here is that the derived neutral will be bonded to ground in the home’s main panel. Since the truck’s neutral is also bonded to ground, it doesn’t address the original issue.
Also, unless the 120-0-120 of truck matches exactly that of the transformer, there will be high circulating currents in the windings with the neutrals connected.

That transformer is intended for use with a generator with a 240V only output.
 
OP
OP

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
152
Reaction score
66
Location
USA
Vehicles
Tesla Model 3
Also, unless the 120-0-120 of truck matches exactly that of the transformer, there will be high circulating currents in the windings with the neutrals connected.
That's one of the things I was wondering about with Pro Power OnBoard. Is there actually significant circulating current to cause problems (e.g. GFCI tripping)?
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,393
Reaction score
4,247
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
That's one of the things I was wondering about with Pro Power OnBoard. Is there actually significant circulating current to cause problems (e.g. GFCI tripping)?
The circulating current won’t affect the GFCI. But it will turn the auto transformer into a big heater!
 
OP
OP

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
152
Reaction score
66
Location
USA
Vehicles
Tesla Model 3
The circulating current won’t affect the GFCI. But it will turn the auto transformer into a big heater!
Theoretically yes. However, it has not been an issue in my experience with 240V split-phase neutral bonded generators. It's probably because the the loads on the 120V legs are never perfectly balanced anyway and the autotransformer has very high rating for neutral imbalance rating.
 

Sponsored

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,393
Reaction score
4,247
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Theoretically yes. However, it has not been an issue in my experience with 240V split-phase neutral bonded generators. It's probably because the the loads on the 120V legs are never perfectly balanced anyway and the autotransformer has very high rating for neutral imbalance rating.
Circulating currents have nothing to do with loads.

If one of these is used successfully with a split phase, neutral bonded generator, I’d bet that only 2 wires - the 240V phases - are connected to anything.

This would also work with ProPower, but simply omitting the transformer, and not running the ground wire from the truck accomplishes the same thing.
 
OP
OP

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
152
Reaction score
66
Location
USA
Vehicles
Tesla Model 3
Circulating currents have nothing to do with loads.

If one of these is used successfully with a split phase, neutral bonded generator, I’d bet that only 2 wires - the 240V phases - are connected to anything.

This would also work with ProPower, but simply omitting the transformer, and not running the ground wire from the truck accomplishes the same thing.
Hmm ... maybe we are saying the same thing. The main purpose of the autotransformer is automatic load balancing between the 120V legs. I don't think you get that connecting directly to Pro Power OnBoard. This is the setup I have used with 240/120V generators without problems:

Ford F-150 Lightning Pro Power OnBoard with Autotransformer -- to work around the bonded neutral issue? 1678042181985


The diagram is from https://shop.pkys.com/autotransformer.html.

I am interested to know if there is anything in the Pro Power OnBoard that would make it not work in the same setup.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,393
Reaction score
4,247
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Hmm ... maybe we are saying the same thing. The main purpose of the autotransformer is automatic load balancing between the 120V legs. I don't think you get that connecting directly to Pro Power OnBoard. This is the setup I have used with 240/120V generators without problems:

1678042181985.png


The diagram is from https://shop.pkys.com/autotransformer.html.

I am interested to know if there is anything in the Pro Power OnBoard that would make it not work in the same setup.
It does load balance by presenting the 120V loads to the genny as a single 240V load.
But it’s not going to solve GFCI tripping.
 
OP
OP

v2h8484

Well-known member
Joined
Mar 3, 2023
Threads
3
Messages
152
Reaction score
66
Location
USA
Vehicles
Tesla Model 3
But it’s not going to solve GFCI tripping.
That's one thing I would like to certain about Pro Power OnBoard. Typically, 240/120V generators only have GFCI on the 120V outlet circuits.
 

d2blake

Active member
First Name
Dave
Joined
Jan 11, 2022
Threads
4
Messages
38
Reaction score
35
Location
Tavistock, Ontario
Vehicles
2010 F150 FX4
Occupation
Engineer/Contractor
Enphase uses a neutral forming transformer in their smart switch. Both their back up batteries and the input from solar are 240 volt with no neutral. I haven’t tried it but it would seem like you could connect pro power in the same manner. I am a month or so from getting my Enphase system operational. Once’s it up and running I will be looking at options to use pro power to charge the Enphase batteries during extended outages with low solar input (ie snow storms).
Have you been able to do this? I’d like to know if I can install a transfer switch between utility and the smart controller2. Then have a micro grid with the truck and enphase battery system/solar.