Grumpy2
Well-known member
- Joined
- Nov 23, 2022
- Threads
- 18
- Messages
- 595
- Reaction score
- 614
- Location
- Central Oregon Coast
- Vehicles
- 23 F150 Pro SR
- Occupation
- Retired Hvy Construction
If this is your only electric panel for the house, and all you have is a main disconnect breaker in the meter box, you need a licensed electrician look over your panel and ignore sunrun.
You appear to have 2 spares that may allow a 240v breaker for your charger, but you need to have this panel & it's incoming wire inspected for capacity. This may be a 100 amp panel, or smaller, and you many not have wire and/or panel capacity for the 50 amp breaker needed for a 40 amp charger.
You appear to have 2 spares that may allow a 240v breaker for your charger, but you need to have this panel & it's incoming wire inspected for capacity. This may be a 100 amp panel, or smaller, and you many not have wire and/or panel capacity for the 50 amp breaker needed for a 40 amp charger.
Sponsored