System is up

Ford F-150 Lightning Charge Station Pro Stops after a few minutes SmartSelect_20240216_131806_FordPass
Sponsored

 
OP
OP

pmac1010

Member
First Name
Patrick
Joined
Jan 10, 2024
Threads
1
Messages
7
Reaction score
3
Location
Atlanta GA
Vehicles
F150 Lightning, Tesla Y LR, Leaf, Porsche Spyder
I think I have fixed my charger. I suspected my electrician used an aftermarket circuit breaker and I was correct. I replaced it with a genuine manufacturer part to match my panel and was able to charge at full power for over 4 hours. We went through 3 different breakers before I came to suspect this. Not being an electrician, I had no idea that sub-standard after market breakers even existed. Lesson learned.
 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
32
Messages
3,609
Reaction score
6,440
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2022 Mach-E Premium
Occupation
Electrician
After market breaker? It's not made by the same company that makes the panel?

Some breakers are interchangeable with some panels. I know Siemens and Homeline breakers are interchangeable with each other.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,599
Reaction score
4,565
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
After market breaker? It's not made by the same company that makes the panel?

Some breakers are interchangeable with some panels. I know Siemens and Homeline breakers are interchangeable with each other.
They fit, but are not likely listed to be used in the other panels.
There are “classified” 1” breakers that are listed for other brands. Eaton is the only one I’ve seen, but there could be others.
I‘ve seen someone try to use a Siemens in a GE (could have been the other way around) and it overheated at the bus stab because the breakers were designed for a slightly thicker bus connection than what the panel had.
 

Grumpy2

Well-known member
Joined
Nov 23, 2022
Threads
18
Messages
694
Reaction score
715
Location
Central Oregon Coast
Vehicles
23 F150 Pro SR
Occupation
Retired Hvy Construction
This video details a charger setup that was done by licensed electrician, according to code, and inspected that failed and could have burnt the house down


Tom's point is the code is behind, the constant full load current demanded to charge EV, loads parts that normally would not fail.