If you have an electrician already coming to the property, look at having a NEMA 14-50 receptacle attached to a 50A breaker. You are supposed to keep constant current below 80% of the breaker capacity, so that would allow a 40A charge. Most EVSE units rated at 40A or below can be purchased with the NEMA 14-50 plug. (Although the cords are usually ridiculously short, so have the outlet installed where you want the EVSE installed.)Hi, looking at possibly getting a Lightning. As for the electrical side, I currently have a 220 outlet for my table saw.
In a few days, we will begin remodeling our kitchen, which will include an induction cooktop, which also requires 220. They will be wiring up a new 100 amp sub panel because my 200 amp panel is maxed out.
Can I adapt my saw circuit for charging and switch back and forth or do I need a third 220 outlet, if that’s possible? Thanks.
If you’re prewiring for a hardwired charger, DO NOT install a GFCI breaker. Or at least there is no need to for it. This was the advice in the early days, but all current UL Listed hardwired EVSE’s on the market have in-built protection and do not need the GFCI breaker, some advise against it.Recommend you have the electrician install a GFCI breaker and prewire for a hardwired charger. You can finish the install after you have the charger.
The built in protection is GFPE, not GFCI. That’s all that UL requires.If you’re prewiring for a hardwired charger, DO NOT install a GFCI breaker. Or at least there is no need to for it. This was the advice in the early days, but all current UL Listed hardwired EVSE’s on the market have in-built protection and do not need the GFCI breaker, some advise against it.
Kinda funny since I myself on this forum early on recommended GFCI breakers to people, depending on which EVSE they were installing. But all the current good ones like Emporia, ChargePoint, Grizzl-e, Tesla all have fault protection in their current model units and some have always had it.
That said, they may be required to install a GFCI breaker to pass inspection if the endpoint is just capped or they assume an outlet will be installed.
So you don’t have dinner in the oven, or soup simmering on the stove, while you’re tinkering in the workshop and cutting things on the saw?I do not think that you have a problem. You do not use your kitchen when you use your saw. Likewise, you do charging overnight when you do not use your saw or kitchen.
I think that is what the electrician was saying, it would be a rare case that we would max out the panel.I do not think that you have a problem. You do not use your kitchen when you use your saw. Likewise, you do charging overnight when you do not use your saw or kitchen.