Hunter
Active member
- Thread starter
- #16
I spoke with my electrician. So to clarify, we have a 200A main box with 90A coming to the house sub-panel. He can't pull anymore because the rest is being used by our upstairs and downstairs HVACs (2 separate units).
He wants to run a 60A breaker off of our house sub-panel to the charger and then pull 48A (with the charger setting on 5).
Thoughts?
(And thanks for everyone's input)
He wants to run a 60A breaker off of our house sub-panel to the charger and then pull 48A (with the charger setting on 5).
Thoughts?
(And thanks for everyone's input)