Is there a safety issue? The truck circuitry is still protected by its built in GFIC and the house is presumably protected by its own circuitry. The truck maintains its own ground as does the house. Is an ungrounded cable an issue when both ends have their own (though different) grounds? Hmmmm.​
The truck end doesn't have a ground, really. The tires are very good insulators. But the truck end has a GFCI, which I suppose would trip if you shorted line to ground through your body while plugging in the cable - because the line and neutral current would be unbalanced, and that's how GFCI's work.

That suggests to me that code to the contrary notwithstanding, a cable like this that simply does not connect ground between the truck and the house is a safe way to work around the issue with transfer switches and bonded neutral, in general. It's just that you - or the electrician who installs a transfer switch or generator inlet for you "behind the meter" - are subject to code and so you are not supposed to do this; but on the utility's side of the demarcation point, NEC does not apply, so they can let you do it there!

There are people here who know a lot more about this than I do. Does the above seem right?
Sponsored

 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
8
Messages
3,225
Reaction score
3,985
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
But the truck end has a GFCI, which I suppose would trip if you shorted line to ground through your body while plugging in the cable
I don’t think anybody in their right mind would switch on ProPower before connecting the cable at both ends.
 
  • Like
Reactions: GDN

GDN

Well-known member
First Name
Greg
Joined
Feb 15, 2022
Threads
84
Messages
3,095
Reaction score
3,671
Location
Dallas, TX
Vehicles
Lightning Lariat ER, Performance Y
Occupation
IT
Simple steps I wrote up and added to my electrical panel documentation - adopt as necessary.

Ford F-150 Lightning Easy way to safely access backup power for home and free (for some PG&E customers) 1720840879042-12
 

dmd3home

Active member
First Name
Dan
Joined
Apr 20, 2022
Threads
1
Messages
30
Reaction score
11
Location
Central Coast CA
Vehicles
Lightning, Spark EV, Tesla Y, BMW X5 phev
Of course the truck doesn't have a "ground" ground....if you know what I mean, but I assume the truck frame is a ground for for the pro power electrical circuitry on the truck (and the 12v too, I guess).
As for the GFI protection, I'm not a "professional", but yes, with 120v circuitry it is looking for any difference between the hot and neutral current flow....showing that some current flow is "lost" somewhere. But with 220v it must be looking at L1 and L2 detecting any difference in current flow between these two hot legs (no neutral involved). A ground wouldn't even necessarily enter in on either GFI circuitry (though there will always be a connected available ground as with any proper electrical circuit). The "generator" cord supplied by PG&E is 220V only.

Again, I'm just very pleased it works!!!!
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
8
Messages
3,225
Reaction score
3,985
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
Of course the truck doesn't have a "ground" ground....if you know what I mean, but I assume the truck frame is a ground for for the pro power electrical circuitry on the truck (and the 12v too, I guess).
As for the GFI protection, I'm not a "professional", but yes, with 120v circuitry it is looking for any difference between the hot and neutral current flow....showing that some current flow is "lost" somewhere. But with 220v it must be looking at L1 and L2 detecting any difference in current flow between these two hot legs (no neutral involved). A ground wouldn't even necessarily enter in on either GFI circuitry (though there will always be a connected available ground as with any proper electrical circuit). The "generator" cord supplied by PG&E is 220V only.

Again, I'm just very pleased it works!!!!
On a 240V, 3 wire circuit, GFCI protection monitors all 3 conductors (L1, N, L2). If the vector sum of all 3 is more than 6mA, it must trip. If the sum is 3mA or less, it cannot trip.

If the cord was “220 only”, you would not be able to properly power 120V loads in your home.
 

Sponsored

YellowGoat

Active member
Joined
Jun 20, 2023
Threads
0
Messages
32
Reaction score
31
Location
California
Vehicles
'23 F150 Lightning Lariat ER
Just got this installed on our house last week. The PG&E person just randomly showed up after I'd applied for it back in April or something. No contact at all prior. No scheduling, phone calls, emails, nothing. I'm NOT in what they labeled a fire zone so I'd just given up and figured they'd ignored my application. In the application I did not see Ford Lightning so I just picked a Ford generator they had listed with about the same output as the truck. Installers didn't seem to care.

Certainly not plug and play. Instructions state to turn off pretty much all your main panel breakers (Main, AC, solar, pool etc), plug in, power truck, then turn just your main back on. Not overly complicated, but not something my wife would feel comfortable doing.

Cable provided indeed does not fit into the outlet in the bed of the truck since it has a comically large molding around the plug that interferes with the outlet cover in the truck. Ordered the aforementioned extension cord.

Haven't tested it yet since we haven't had a power outage. Even PG&E said they could not test it since that would require taking out power to the whole neighborhood (I told 'em I was fine with that but they just laughed :) ). I'll make an update if anything breaks / catches fire when I get a chance to try.

This certainly saves me the headache of having a generator port installed and I'd been waiting (a year now) to install the Charge Station Pro to see if I'd need to. (I've managed to go a year just charging it off a 110 in the garage with DCFC top off once or twice a month which surprised me and is probably a topic for a whole 'nother post.)

Anyways, point being, if you apply for one and don't hear anything, they're probably just taking their sweet time. And don't fret about the fire zone req or listing a generator. That doesn't seem to disqualify you.
 
OP
OP

Wsh68

Well-known member
Joined
Apr 18, 2022
Threads
9
Messages
96
Reaction score
141
Location
Arroyo Grande
Vehicles
2022 Lariat ER, Tesla Model Y
Just got this installed on our house last week. The PG&E person just randomly showed up after I'd applied for it back in April or something. No contact at all prior. No scheduling, phone calls, emails, nothing. I'm NOT in what they labeled a fire zone so I'd just given up and figured they'd ignored my application. In the application I did not see Ford Lightning so I just picked a Ford generator they had listed with about the same output as the truck. Installers didn't seem to care.

Certainly not plug and play. Instructions state to turn off pretty much all your main panel breakers (Main, AC, solar, pool etc), plug in, power truck, then turn just your main back on. Not overly complicated, but not something my wife would feel comfortable doing.

Cable provided indeed does not fit into the outlet in the bed of the truck since it has a comically large molding around the plug that interferes with the outlet cover in the truck. Ordered the aforementioned extension cord.

Haven't tested it yet since we haven't had a power outage. Even PG&E said they could not test it since that would require taking out power to the whole neighborhood (I told 'em I was fine with that but they just laughed :) ). I'll make an update if anything breaks / catches fire when I get a chance to try.

This certainly saves me the headache of having a generator port installed and I'd been waiting (a year now) to install the Charge Station Pro to see if I'd need to. (I've managed to go a year just charging it off a 110 in the garage with DCFC top off once or twice a month which surprised me and is probably a topic for a whole 'nother post.)

Anyways, point being, if you apply for one and don't hear anything, they're probably just taking their sweet time. And don't fret about the fire zone req or listing a generator. That doesn't seem to disqualify you.
Glad to see another one of us finding solutions and our trucks. I was explaining this all to my Brother in law tonight as he is looking for a decent solution to backup power during fire outages in the Sierra foothills.
 

Iroc34a

Well-known member
First Name
Roc
Joined
May 17, 2024
Threads
8
Messages
74
Reaction score
29
Location
Illinois
Vehicles
23 Lightning Platinum
Occupation
Mechanic for American Airlines. GSE (ground equipment) 37 years. Worked on everything from Lawn mowers to Boeing 747's.
PG&E BU power cord.jpg
OK, here's the back up power cable supplied by PG&E....it has a standard twist-loc plug for connecting to the Lightning and, what I assume is a standard generator input connector on the other end. Yes, there are four conductors at each end of the cable....L,N,L, and ground. I checked continuity through the cable for each conductor and found that YES, as was speculated by some, the ground conductor DOES NOT PASS THROUGH THE CABLE FROM THE LIGHTNING TO THE METER CONNECTOR. There is actually just L-N-L making the connection....no ground! And yes, as this connects right to the meter, upstream from your main breaker and panel, no ground is required.This must be why it's working with no GFIC tripping problems. It just works!​
Is there a safety issue? The truck circuitry is still protected by its built in GFIC and the house is presumably protected by its own circuitry. The truck maintains its own ground as does the house. Is an ungrounded cable an issue when both ends have their own (though different) grounds? Hmmmm.​
I'm guessing that PG&E, being a large electric utility, has thoroughly looked at this. I'm just pleased that it works and is a great and easy solution to what I thought was going to be a difficult problem. Thank you PG&E.​
So , I am thinking that if this cable fits into the Generlink, it should work?
 

Iroc34a

Well-known member
First Name
Roc
Joined
May 17, 2024
Threads
8
Messages
74
Reaction score
29
Location
Illinois
Vehicles
23 Lightning Platinum
Occupation
Mechanic for American Airlines. GSE (ground equipment) 37 years. Worked on everything from Lawn mowers to Boeing 747's.
Well from what I gathered; this cord will not fit the Generlink. Lock is different. So, I sent an email to TESCO about how to go about purchasing their BPTM. Maybe my electric company in Southern Illinois, which has approved the Generlink will allow the TESCO model? We shall see, hopefully a positive response. Ill update as soon as I hear anything.
 

Big guy

Member
First Name
Bill
Joined
Apr 3, 2023
Threads
0
Messages
17
Reaction score
8
Location
Illinois
Vehicles
2009 Ranger, 2008 Shelby GT, 2013 Ford Edge
Occupation
Retired
Well from what I gathered; this cord will not fit the Generlink. Lock is different. So, I sent an email to TESCO about how to go about purchasing their BPTM. Maybe my electric company in Southern Illinois, which has approved the Generlink will allow the TESCO model? We shall see, hopefully a positive response. Ill update as soon as I hear anything.
 

Sponsored

Big guy

Member
First Name
Bill
Joined
Apr 3, 2023
Threads
0
Messages
17
Reaction score
8
Location
Illinois
Vehicles
2009 Ranger, 2008 Shelby GT, 2013 Ford Edge
Occupation
Retired
Has anyone confirmed which company is making the PGE unit (model) so we can try to source it for our Homes not using PGE somewhere else in the country.
 

Iroc34a

Well-known member
First Name
Roc
Joined
May 17, 2024
Threads
8
Messages
74
Reaction score
29
Location
Illinois
Vehicles
23 Lightning Platinum
Occupation
Mechanic for American Airlines. GSE (ground equipment) 37 years. Worked on everything from Lawn mowers to Boeing 747's.
Has anyone confirmed which company is making the PGE unit (model) so we can try to source it for our Homes not using PGE somewhere else in the country.
From what I have seen . Tesco
 

Big guy

Member
First Name
Bill
Joined
Apr 3, 2023
Threads
0
Messages
17
Reaction score
8
Location
Illinois
Vehicles
2009 Ranger, 2008 Shelby GT, 2013 Ford Edge
Occupation
Retired
Terrific info. I never saw this before. I will need to contact Teso and my local power company. This is
obviously the best solution to use our Lightnings during power outages. Thanks for posting this.