dodgedak
Member
- Thread starter
- #1
I recently had the FCSP installed with a 100 amp breaker and a 25 feet run with the #3 wires by a licensed electrician and it is installed inside the garage.
First day when it started charging it was shutting down and restarting multiple times. I contacted support and they mentioned I had an older firmware .64 and had to have the new .91 firmware installed to avoid the overheating issue and the quickest way to do this was to reset the circuit breaker which I did and was able to get the .91 firmware. After this I thought the problem would go away but it has only reduced the number of restarts, charger charges at 16 or 17Kw rate for approx 50-55 minutes and then it restarts and again ramps up to 17kw. I called the ford BEV support and they say it is operating fine, as long as it does not stop charging ignore the restart messages and it should continue to finish the charge. Also suggested placing a pedestal fan next to charger so that it does not overheat. Which seems preposterous. If temp was the issue i tried charging early morning when the temp was in the 60's and still the same issue. Any thoughts/feedback ?.
I have yet to derate it to 72 or 64 amps by turning the setting from 7 to 6 or 5, will have the try that. But the main purpose of spending money to install this was to get the full rate but Ford is not helping by saying this is a normal behavior.
edited: to update actual breaker amp. It is a 100 amp breaker.
First day when it started charging it was shutting down and restarting multiple times. I contacted support and they mentioned I had an older firmware .64 and had to have the new .91 firmware installed to avoid the overheating issue and the quickest way to do this was to reset the circuit breaker which I did and was able to get the .91 firmware. After this I thought the problem would go away but it has only reduced the number of restarts, charger charges at 16 or 17Kw rate for approx 50-55 minutes and then it restarts and again ramps up to 17kw. I called the ford BEV support and they say it is operating fine, as long as it does not stop charging ignore the restart messages and it should continue to finish the charge. Also suggested placing a pedestal fan next to charger so that it does not overheat. Which seems preposterous. If temp was the issue i tried charging early morning when the temp was in the 60's and still the same issue. Any thoughts/feedback ?.
I have yet to derate it to 72 or 64 amps by turning the setting from 7 to 6 or 5, will have the try that. But the main purpose of spending money to install this was to get the full rate but Ford is not helping by saying this is a normal behavior.
edited: to update actual breaker amp. It is a 100 amp breaker.