I finally got my truck on Monday, so I scheduled an electrician to come out next week to install a JuiceBox 40 plug in charger, which I have already bought. This is the description they wrote in my estimate, just wanted to double check that everything makes sense to you guys. It obviously will include a plug, which isnt mentioned, but moreso I wanted to double check the wiring reqs and breaker reqs. Thanks
Installation of 1 circuit from the main service panel located in
the basement of the home. This circuit will follow an HVAC
bulkhead from the panel room to the adjacent maintenance
room. This room shares a wall with the garage above where the
customer provided charger will be installed. The wire being
used for this installation will be 6-3 MC cable. This wire is being
used for the future possibility of a faster charger being
installed. But for the use of the charger being provided by the
customer we will install a 50 amp breaker on this #6 copper
wire.
Installation of 1 circuit from the main service panel located in
the basement of the home. This circuit will follow an HVAC
bulkhead from the panel room to the adjacent maintenance
room. This room shares a wall with the garage above where the
customer provided charger will be installed. The wire being
used for this installation will be 6-3 MC cable. This wire is being
used for the future possibility of a faster charger being
installed. But for the use of the charger being provided by the
customer we will install a 50 amp breaker on this #6 copper
wire.