Branch circuits serving EVSEs must be sized such that they are only loaded to 80%. The 80A FCSP would thus require a 100A circuit to be used at 80A. I wouldn’t expect that going to #3 would require larger conduit. What size are you running?Interesting website. I referenced the wire manufacturers site and got #4 @ 75C. Also I trust the electrician who wired for it at my WA home. He used #2 AL Service Entrance Cable, but would have used #4 CU if I wanted to pay for it.
If I have to go #3, I will need bigger conduit and will have to use ugly ass PVC.
Now I am triple guessing the choice