Depends on what you mean by two breakers. You refered to the the main as four breakers but it is really two 2-pole breakers together in one. If it is two poles or two whole positions together, that is making it a higher voltage (240) at the same current, because positions alternate between 120V legs.
This is the main breaker for incoming to the panel
Ford F-150 Lightning Pro Charging Station to NEMA 14-50 20220305_152950


And here is a picture of the two spare 50 A (middle of the right side)
Ford F-150 Lightning Pro Charging Station to NEMA 14-50 20220305_152736
 

MickeyAO

Well-known member
First Name
Mickey
Joined
Apr 2, 2020
Threads
25
Messages
1,039
Reaction score
2,014
Location
San Antonio Tx
Vehicles
Rapid Red Lightning Lariat ER, Kia EV6 GT-Line AWD
Occupation
Retired Lab Manager of the Energy Storage Technology Center
I think that's a single 2 pole 50A breaker. You may be able to replace it with a 100A breaker, but as it is, it's only 50A.
Thanks! I know DC and batteries, but I guess that type of knowledge doesn't transfer to AC currents ;)
 

shutterbug

Well-known member
First Name
Joseph
Joined
May 20, 2021
Threads
7
Messages
1,242
Reaction score
1,221
Location
Phoenix
Vehicles
MME GB FE—Dead. F150L Lariat SR. MME Rally.
If they make a compatible slim line model in 100A
Yes. That's why I said "may". Still, need to talk to a qualified electrician. Looking at this panel it has a 100A circuit for the stove. That seems high. Most modern stoves need a 50A circuit. So there may be an opportunity there. Talk to an electrician.
 

Sponsored

MickeyAO

Well-known member
First Name
Mickey
Joined
Apr 2, 2020
Threads
25
Messages
1,039
Reaction score
2,014
Location
San Antonio Tx
Vehicles
Rapid Red Lightning Lariat ER, Kia EV6 GT-Line AWD
Occupation
Retired Lab Manager of the Energy Storage Technology Center
Yes. That's why I said "may". Still, need to talk to a qualified electrician. Looking at this panel it has a 100A circuit for the stove. That seems high. Most modern stoves need a 50A circuit. So there may be an opportunity there. Talk to an electrician.
Definitely not a modern home. House built in the '60s, stove bought new probably 20 years ago, and panel upgraded 10 years ago. Lived in the house for 26 years.
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
169
Messages
12,134
Reaction score
12,778
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow & 2024 Harley-Davidson Road Glide CVO-ST
Occupation
Retired
deleted
 
Last edited:

fromport

Member
Joined
Jun 5, 2021
Threads
0
Messages
5
Reaction score
0
Location
93022
Vehicles
2010 gmc sierra, 2020 &2023chevy bolt, 2xNEV
Occupation
engineer
Another thing I have not seen mentioned is that you CANNOT precondition the vehicle (at least the Mach-e) on a 120V EVSE. There just isn't enough power to pre-heat the battery. There isn't even enough to heat the cabin - it pulls from the battery if you ask for a remote start. Our EVSE had a fault (Grizzl-e replace on warranty) and we had to rely on the Ford mobile EVSE on a 120V circuit. It was not fun, and I would never own an EV without 240V charging available at home.
The RAV4EV I once drove with tesla technology was able to charge at 120 volt @ 30 amps so 3600 watt. Normally the supplied "trickle charger" with the car limits the current to 12 amps @ 120V = 1440 Watt. But there are exceptions.
 

Deleted member 9341

Guest
The RAV4EV I once drove with tesla technology was able to charge at 120 volt @ 30 amps so 3600 watt. Normally the supplied "trickle charger" with the car limits the current to 12 amps @ 120V = 1440 Watt. But there are exceptions.
I was able to precondition a BMW i3 with one as well
 

adoublee

Well-known member
Joined
Aug 30, 2021
Threads
12
Messages
749
Reaction score
683
Location
Midwest
Vehicles
2 EVs
And here is a picture of the two spare 50 A (middle of the right side)
20220305_152736.jpg
I wouldn't make any decisions until you verify those "labels". Typically you would want to see a spare in the off position to know it isn't being used - you might turn off and confirm nothing is affected. The 100A breaker for "stove" is suspect (larger than typical) as is 50/2 "house" breaker.
 

Sponsored

jefro

Well-known member
Joined
Oct 28, 2021
Threads
3
Messages
699
Reaction score
231
Location
Texas
Vehicles
F150, Corvette, Bolt EV,
I have a number of slim 240V breakers in my panels. Just none 100A. I had to move stuff around to get some to match to two legs. Since there are slim breakers in we have to believe it is supported.

Good catch on both the labels and the 100A stove.

My i3 and Bolt will try to condition at 120VAC but the load would exceed the supply and the rest came from battery. Not sure if MME would decide to refuse power.
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
169
Messages
12,134
Reaction score
12,778
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow & 2024 Harley-Davidson Road Glide CVO-ST
Occupation
Retired
I have a number of slim 240V breakers in my panels.
Could you post a photo of what they look like?

I'm curious to see how it would be set up, I'm imagining two slim groups with a breaker tie across all four switches, if any of the four breakers (or 240 groups) experience an excessive load all will trip off.
 
OP
OP

DrZoidberg

Well-known member
Joined
Jun 21, 2021
Threads
4
Messages
221
Reaction score
163
Location
SATX
Vehicles
Lightning Eternal Vestibule
Dumb question. Could this plug into my dryer outlet in the garage,
 

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
169
Messages
12,134
Reaction score
12,778
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow & 2024 Harley-Davidson Road Glide CVO-ST
Occupation
Retired
 





Top