Sorry, but are you planning to install '60 vintage EVSE?What about things that were to code in 1960 when a house was built, but certainly not there currently?
Sponsored
Sorry, but are you planning to install '60 vintage EVSE?What about things that were to code in 1960 when a house was built, but certainly not there currently?
No, I already have two 30 amp EVSEs in the unfinished garage with 8 guage Romex.Sorry, but are you planning to install '60 vintage EVSE?
The 100A Pro Charger will not "plug into" anything--it doesn't terminate in a plug. Within the first few responses to your original question, someone mentioned that you could retrofit a plug to the wires and plug it in (to your 14-50).Dumb question. Could this plug into my dryer outlet in the garage,
This is incorrect. There are good reasons for the continuous load rating.and I don't mean to discount what people might read in the 'code', but my experience over many years does not negate what the breaker size SAYS on the breaker, itself. If it's a 50amp breaker, it's designed to handle 50amps of power, that's why it says so. If the code did not allow it to, it would not be allowed to be printed on it. Have fun! It's not really that complicated.
I probably should have clarified.The 100A Pro Charger will not "plug into" anything--it doesn't terminate in a plug. Within the first few responses to your original question, someone mentioned that you could retrofit a plug to the wires and plug it in (to your 14-50).
That plan, however, creates a few issues: the wires coming from the 100A charger are going to be massive compared to any regular plug you find at a DIY supply store (it's not an aesthetic issue--you may well find the gauge of the wires is so different that there aren't approved connectors for them; that's intentional in order to prevent this kind of wiring bootlegging), the ground/neutral of a hardwired system won't match the plug's (hardwired tend to have 2+1g whereas the NEMA outlet you're asking about will be 3+g and you'll be missing a neutral wire), these types of outlets (both the 14-50 and whatever dryer outlet you have) aren't rated for consistent plug/unplug cycles. The last two factors are why EV installers tend to "frown" on such installs as someone mentioned.
The problem with hiring someone to do this work is that a licensed electrician doing permitted work is unlikely, in my experience, to listen to the customer who wants to install a wire run that can handle 100A but then put a 60A breaker on end and tie it to a 50A outlet and then plug in a 100A EVSE. If the amps the EVSE can be charged at aren't user adjustable you might get someone to go along with that install, but if it's simply controlled by the app then I can't imagine someone touching that with a ten-foot pole. Not because the code says no, but because their liability insurance and good business sense will tell them no.
After that's all installed and you intentionally (because you don't know better or don't care) or accidentally (because it's an easy slider in the app) there isn't anything preventing the system from becoming a fire risk. That's the simplest explanation for why electricians tend to wire things up to the lowest common denominator where someone is physically limited from accidentally plug something in wrong (shape of the plug compared to outlet) or try to indicate that the outlet not be mis-used (some older installs just did whatever, then electricians started labeling 14-50s as "for EVSE ONLY," and some just went ahead and laid an extra wire).
When it's all said and done, after you've finally convinced someone to do all this work what you'll likely find is that you have a 100A EVSE on a circuit that can't handle more than 50A and that you better hope it's too difficult to adjust the current (or that the device itself doesn't fail). OR you have an overbuilt (and expensive) 100A circuit for an EVSE that will never need to go above 30A to suit your needs.
Keep in mind, all of this headache is circumvented by using the 120/240 EVSE also provided for free by Ford, which does plug into a standard outlet, a 20A outlet (which are often found in garages), the dryer outlet you're asking about, and a 14-50 outlet that your landlord already approved...and all for a fraction of the size of the relatively huge/bulky 100A charger.
^^ This right here. There are going to be fires. Make sure your 'paperwork' is in order.One of the downsides of EV adoption is going to be housefires. Why? Because of many reasons, some of which are identified in this thread. People are going to plug into dryer outlets not designed for the load, and wires are going to overheat, and houses are going to burn. That's just reality.
I strongly recommend to anyone that asks me about installing an EV charger, or outlet for a charger, that they both hire an electrician AND insist on an inspection.
I've been under the impression you intended to use the 100A EVSE this whole time! If you're only intending to use the 120/240v "mobile" charger it'll have a 14-50 plug on the end.I probably should have clarified.
I don't think I'll be installing the pro since I'm in a short term rental. I was referring to the mobile charging unit that comes with it, does that just plug into a dryer outlet is it the same plug?
Nothing requires anything that was installed per code in effect at the time it was installed to be brought up to current. There are a couple of obscure exceptions. I’ve fought this with home inspectors a couple times even though they should know better.What about things that were to code in 1960 when a house was built, but certainly not there currently?
In most cases, it can be determined what things looked like. The entire run of the circuit is unlikely to have been completely destroyed, so it's likely they can determine what was there and what wasn't.What about things that were to code in 1960 when a house was built, but certainly not there currently?
Correct in most cases, and permit trails (where required) help to identify what was in effect at the time. The one exception - in some jurisdictions - is where unpermitted work was done. Let's say that 20 years ago someone added a circuit to the home but never pulled a permit, and it doesn't match current code - some AHJ's can require the addition to be ripped out, or brought up to current code.Nothing requires anything that was installed per code in effect at the time it was installed to be brought up to current. There are a couple of obscure exceptions. I’ve fought this with home inspectors a couple times even though they should know better.
Anything you add today must meet today’s code. Some repairs can be done as-is but some are required to be brought up to current code. A licensed electrician will know all the nuances and exceptions.
Yeah…permits here are only required for totally new construction. We have no trail!Correct in most cases, and permit trails (where required) help to identify what was in effect at the time. The one exception - in some jurisdictions - is where unpermitted work was done. Let's say that 20 years ago someone added a circuit to the home but never pulled a permit, and it doesn't match current code - some AHJ's can require the addition to be ripped out, or brought up to current code.
Now - in my county, electrical permits are not required... and in the county east of mine, they still don't use building permits. It's rather difficult to enforce anything here, but insurance companies can still try.