Well-known member
You’re oversizing the wire. For THHN in conduit, #8 is sufficient for 50A. I just bought #8 copper for $0.47 per foot.The limiting factors are the 30 amp dryer breaker which will trip eventually as the mobile charger will pull 30+. Then the feed from the panel to the dryer needs to be at least AWG 8 copper (not Aluminum) to pull the 32 amp peak of the mobile charge.
This is why you hire a trained electrician. You’ll need to upgrade the panel breaker to at least 40 amp.
Also, my mobile charger went red light of death at 40,000+ miles in the MME. I switched to CP Home Flex that charges at about 9 KWh and can easily replace 90 miles in 5 hours.
I sat down and did some calcs on relocating the charger such that I can do inside or outside charging (summer outside and run the plug-in side through a small pass thru door) and realized that to take full advantage of the CP Home Flex max out put I’ll need a 50 Amp breaker and 35’ + of AWG 6 and realistically I’ll probably go to AWG 4 as the run is nearly 40’. That 40’ of AWG 4 copper is not cheap. And the run needs to be in conduit and the cost of that simple extension is likely $3,000. Since our garage is separately metered from the house that makes the upgrade easier except the 100 amp utility panel installed by the former owner has 300 amps of breakers! 🫣 because garage apartment with stove/baseboard heat/hot water tank! Switching out the utility panel for a 300 amp is $$$.
So.. be warned. Nothing comes cheap or easy.