Ford Charge Station Pro.The names and how they are different is very confusing. Which one comes from Sunrun with the ER?
Confusing names is Ford's #1 business.
Sponsored
Ford Charge Station Pro.The names and how they are different is very confusing. Which one comes from Sunrun with the ER?
At one time, everything “Pro” was targeted for fleet customers exclusively. No longer.Ford Charge Station Pro.
Confusing names is Ford's #1 business.
If you run 4-2, you can step up to an 80A breaker, and then derate the FCSP to 64A. I would not sell the Ford -- as much as some folks have had trouble, most people get the kinks worked out. Is there a reason you don't want the full 80A? Afraid you would overload your main panel? I cannot think of any other reason. If you have an existing 6-2 wire to a decent location, that would be a good reason too I guess.
It is derated via a dial selector buried inside the case. No one will accidentally change that setting without being knowledgeable enough to trust themselves with opening the case and messing with the internals. Not likely. Label is of course not a bad idea.
Faster charging is nice.
You can set the charge rate in the app lower, but not higher than the hardware setting.I read earlier about someone turning charging up to 80 amps, but I'm assuming, what is above is true. When I self installed for our Solar charger, I derated to 12amps with the dial, as it's on a 6kW Hybrid charge/verter. I know there is a setting in the app to change amperage, but, I'm assuming it can't override the dial setting.
Anyone think this is not true ?
I was trying illustrate one's options with the FCSP. 6/2 wire for 50A Breaker>>derated to 40A continous. 4/2 wire for up to 80A>>64A continuous. 3/2 for 100A>>80A Continuous. Perhaps my original post was not clear, though I think it was. The derating thing gets confusing, especially since a derated 100A circuit charges at 80A, and an 80A circuit is also an option (charging at 64A)I don't have the install manual in front of me but I believe Ford calls for 3g wire not 4... I'm pretty confident of this because my guy couldn't source 3g so mine's running on (more expensive) 2g. Nothing wrong with oversizing wire, just don't want to undersize.
Sure, I absolutely understand what you're saying, but anything less than 3g is 'out of spec' and not approved for use with the FCSP (which is why I suggested selling it and buying one rated for the available power). I'm not an electrician or engineer, nor am I trying to start an argument. I just RTFM which says:I was trying illustrate one's options with the FCSP. 6/2 wire for 50A Breaker>>derated to 40A continous. 4/2 wire for up to 80A>>64A continuous. 3/2 for 100A>>80A Continuous. Perhaps my original post was not clear, though I think it was. The derating thing gets confusing, especially since a derated 100A circuit charges at 80A, and an 80A circuit is also an option (charging at 64A)
Hope this makes it clear.
Though I am not absolutely certain (like, I would have to verify real world, and have not done so) I am as close to certain as I can be that the internal dial selector CANNOT be overridden via software. I would think such a feature would border on engineering malpractice. (That term exists BTW)
This is a really interesting point, which I have to agree with. Although I think it stems from a poorly-written manual.Sure, I absolutely understand what you're saying, but anything less than 3g is 'out of spec' and not approved for use with the FCSP (which is why I suggested selling it and buying one rated for the available power). I'm not an electrician or engineer, nor am I trying to start an argument. I just RTFM which says:
>e)Use 3 AWG, 90°C copper wire only for AC connections (A/L1 and B/L2[N])
-and-
>g) CAUTION to reduce risk of fire, connect only to a circuit with 100 amperes maximum branch circuit overcurrent protection in accordance with the National Electric Code, ANSI/NFPA 70.
This is from the PDF I attached earlier in the thread. While it does tell you how to adjust the internal potentiometer to derate the unit, it *does not* say you can run it on thinner gauge wire and do this safely. Yes it *can* be done the way you describe, but again, that's not a use case specified by Ford, and no, there is no software change that would override the internal setting.