Nikola 369
Well-known member
The panel is square D panel and the breakers were relocated from main (also Square D )panel. The drum switch is UL listed and rated 380VAC 63Amps, so good fit for 240VAC 30Amps from lightning.Not too sure about the quality of an 8 circuit panel with breakers for $28.
The nice thing about the lockout plate is you're using all your original panel and breakers. Just adding 2 circuit breakers to the panel and an inlet receptical.
That drum switch might be fine for a boat or rv, but I doubt anything you listed is UL rated for a home.
Heck a few 12 gauge extensions cords will work as needed with no rewiring, just a bit of leg work.
Rick
As for being approved for home use. Many local inspectors are not approving the generator lockout metal slider, it is up to them. The problem with this idea is it requires you to use the breakers as switches……..up through 30amp most breakers are SWT rated (switch rated). The main in your panel is not and this leads to a weak spring tension in breaker. Later the weak spring tension gets hot and can cause a fire. I literally did an inspection for an insurance company, when I was an electrician, for this very reason. Breakers are’nt switches, this is why most inspecrors require transfer switches. After I finished my install, local inspector did inspection and check paperwork of items used, setup was approved.