- First Name
- CHRIS
- Dec 16, 2022
- alexandria virginia
- 2001 FORD RANGER, 2023 F-150 LIGHTNING
Somehow I got the FCSP software update recently without resetting anything, long overdue, but now things work better.I think everyone goes through this headache when your charger is installed. For some reason the charger has to have the latest firmware installed and the 2 ways this can happen is by “forcing it” to try to install it faster by turn off your breaker for 10+ minutes and then turning it back on and checking the charger or by supposedly waiting for that update to finally reach your charger over night through “over the air” update from Ford. I found the easiest way to get it to update faster is by turning the breaker off a few times for 10+ minutes each and it eventually worked like it was suppose to.
My FCSP was never reaching the 48A rate - more like 40A most of the time charging between 60% and 80% so not at the slow down threshold over 90%. I could not get the FCSP added to FordPass until the update came so I could not set the max amps to 48A until then. When I looked at the app and the max amps it was not set at 48A, so I changed it and the first charge after that went much faster.
Figure your load amps, multiply by 125% for a continuous load (the FCSP and all EVSE's are), size the wire to safely carry that current and install a breaker for that amperage.
So if you want to have the full 80A of the FCSP, 80 x 125% = 100A wire and breaker, #3 copper hots #6 ground, and leave the current dial on the FCSP at the max 80A (switch position 7).
For 48A, 48 x 125% = 60A wire and breaker, #6 copper hots #10 copper ground on a 60A breaker, and turn the dial down in the FCSP to 48A setting (switch position 5).
The switch position on the circuit board should be set to correspond to the branch circuit protection per NEC (according to the FCSP install guide) which for the 100A circuit is the 80A setting and for the 60A circuit is the 48A setting per the guide.
Another rule of thumb based on the code: The breaker should never be larger than the current carrying capacity of the wire. Kind of a duh, eh?
EDIT: I am assuming a reasonable distance and voltage drop - if over 150ft say, larger diameter wire might be needed to minimize the voltage drop, but the terminals in the FCSP are only rated for #3 Hot/#6 ground so might need a sub-panel I suppose...but an electrician would know best.
Disclaimer
The information provided in this post is provided for information purposes only and does not constitute any endorsement or recommendation. No warranty, expressed or implied, is made regarding the accuracy, adequacy, completeness, legality, reliability, or usefulness of any information found in this post. It is your responsibility to verify and investigate this information.