Don’t have charger yet, but what I’m doing.You can run aluminum and transition to copper in a junction box near the EVSE.
Sponsored
Don’t have charger yet, but what I’m doing.You can run aluminum and transition to copper in a junction box near the EVSE.
Maybe there’s something more complicated about your installation, but a $5 4-square box and an extra 30 minutes labor should be less expensive than copper wire for are run of any significant distance.He agrees, that is one possibility. He thinks (mostly due to minimum purchase amounts) that the added cost of the junction box and labor almost negates the cost savings, though. So I'm probably going with copper.
I do wish shopping for a competent electrician was easier.
It's low, but in line with the US's long history of randomness in electrical systems.If that’s actual measured voltage, it’s pretty low.
ANSI C84.1 dictates voltage tolerances. Many utilities seem to ignore this. When the first Mach-Es were delivered, there were a lot of people in the Chicago area who couldn’t charge because their utility voltage was way too high - 258-260V. ComEd basically told them to pound sand so Ford provided a software update to accept the higher voltages.It's low, but in line with the US's long history of randomness in electrical systems.
In the northeast, it's not uncommon to find 220V systems around (110V), in fact you'll find on this very forum a lot of people talking about "220". "220, 221, whatever it takes..."
I'm surprised to see it in Hartford, WI (the poster's location listed) but it can also be for many other reasons. My home is 248V, because I'm only a couple of miles from a substation that needs to feed very long runs out to rural farms, where voltage needs to be kept up to minimum specs at the end. For a while, they had it up to 252 and my protection gear started kicking in.
It is, indeed, low, and that means longer charging times for someone at 220V vs. 240V (about 8% less power, so that much longer).
Sure, but many of these grids pre-date ANSI standards (which are +/- 5% of 240VAC RMS, or 228V-252V for those not familiar with the standard) and I don't see ANSI stepping up to fund rebuilds of chunks of the grid where 220V was the original voltage and will likely be for a very long time.ANSI C84.1 dictates voltage tolerances. Many utilities seem to ignore this. When the first Mach-Es were delivered, there were a lot of people in the Chicago area who couldn’t charge because their utility voltage was way too high - 258-260V. ComEd basically told them to pound sand so Ford provided a software update to accept the higher voltages.
Good point about the historical aspect of compliance - I hadn’t thought about that.Sure, but many of these grids pre-date ANSI standards (which are +/- 5% of 240VAC RMS, or 228V-252V for those not familiar with the standard) and I don't see ANSI stepping up to fund rebuilds of chunks of the grid where 220V was the original voltage and will likely be for a very long time.
Not sure of the chargers used in the Ford, but the chargers in the Tesla use switching power supplies and have ratings of 85-265V, so seems ok that they'd up the software if it's found to be ok.
Tesla cars will accept higher voltages but will clip the amperage so that the power limit is not exceeded. For example, my car which allows for 72A at 240V will only charge at up to 69A at 250V to stay below the 17.28 kW power level. IMO, that's way too conservative because the charger electronics are built around current and not small variations in voltage, but it is what it is.
It would more likely be a 8x8 junction box plus lugs for the wires and 2 extra connectors so about $80-$100 in parts. It would likely be closer to an hour labor once you factor in putting everything in, drilling the holes, making the connections, ect.Maybe there’s something more complicated about your installation, but a $5 4-square box and an extra 30 minutes labor should be less expensive than copper wire for are run of any significant distance.
My experience has been that there isn't that much difference between the two. There is *some* savings in using AL for long runs, but it's really not that much and the junction is rather ugly IMO, along with more things to go wrong. The AL/CU lugs (probably Polaris connectors) are $20 ea. at my price.Also don't forget to carry the same current aluminum wire is a larger size (not sure exactly as I dont have a table in front of me and rarely deal with larger sizes). Anything less than about a 50' run would end up costing more.
The power supply is in the vehicle charger itself, and will be a switching supply - I can guarantee there won't be a linear supply in a truck charger. The question is just for how much of a range was the power circuitry designed? I have seen people run Tesla's internal chargers at 277VAC (L1-N on a 480VAC Wye 3ph system), but it violates warranty (and if I recall correctly, the circuitry in the wall connector went poof in relatively short order).Ford likely doesn't make the power supply. It is probably from Siemens like the pro wall charger. They wouldn't redesign a power supply so would likely use an off-the-shelf switching power supply to keep costs and R&D lower.
You end up with something like this, though, note, this is all #3 copper in this box - the Al will be bigger, stiffer, generally less pleasant to deal with. Once you put 3 big Polaris connectors in there there will not be a ton of space left (sorry, I didn't take another shot before buttoning this back up). On the other hand you will have one gozinda and one gozowda rather than two gozowdas and a signal cable as you'll see here. You can get it in a 6x6 box with the Polarises but you won't be able to leave much slack for any future revisions, so you may curse yourself for not going 8x8 later.It would more likely be a 8x8 junction box plus lugs for the wires and 2 extra connectors so about $80-$100 in parts. It would likely be closer to an hour labor once you factor in putting everything in, drilling the holes, making the connections, ect.
Also don't forget to carry the same current aluminum wire is a larger size (not sure exactly as I dont have a table in front of me and rarely deal with larger sizes). Anything less than about a 50' run would end up costing more..
Junction boxes are sized based on conduit size. NEC basically requires the dimension to be a minimum of 8 X the conduit trade size, so 1” pipe means 8” minimum.You end up with something like this, though, note, this is all #3 copper in this box - the Al will be bigger, stiffer, generally less pleasant to deal with. Once you put 3 big Polaris connectors in there there will not be a ton of space left (sorry, I didn't take another shot before buttoning this back up). On the other hand you will have one gozinda and one gozowda rather than two gozowdas and a signal cable as you'll see here. You can get it in a 6x6 box with the Polarises but you won't be able to leave much slack for any future revisions, so you may curse yourself for not going 8x8 later.
If they are part of a listed load-sharing system and coordinate their load management together (as the two pictured units do), then it is permitted. It's not so much "an EVSE", but rather just "EVSE" ("Electric Vehicle Supply Equipment").The NEC does not permit 2 EVSEs on one branch circuit as shown in your picture.
I know that the listed load management feature allows reducing the feeder size and the load used for load calculation, but I still thought that each unit required its own disconnect and branch circuit.If they are part of a listed load-sharing system and coordinate their load management together (as the two pictured units do), then it is permitted. It's not so much "an EVSE", but rather just "EVSE" ("Electric Vehicle Supply Equipment").
In this case, the configuration pictured is specifically laid out in the manual for the (Listed) equipment.I know that the listed load management feature allows reducing the feeder size and the load used for load calculation, but I still thought that each unit required its own disconnect and branch circuit.
625.40 requires “an individual branch circuit.” To me, that means 1 branch circuit for each piece of equipment.
But, I’ve been wrong before!
Conduit size is part of the equation, but junction boxes are based on a box fill calculation. It also takes into account the number of conductors and the method of connecting the wires together. Split bolts, wire nuts etc.Junction boxes are sized based on conduit size.