RickKeen
Well-known member
- Thread starter
- #1
Had my emporia 48 amp hard-wired charger install inspected today (and passed). The inspector had a couple of comments that may be helpful to others.
1. He was glad to see 60 amp wiring. He indicated that even though the emporia is adjustable, the adjustment is in the app and too easy for the user to just dial it up. He said only for models of chargers where the current limit is set by switches or jumpers inside the box would he pass a setup with wiring rated lower than the max setting on the charger.
2. In regards to peak load, he mostly worries about things like the hot tub and air conditioning that can turn on anytime by themselves. Was not concerned about the welder and oven outlets for peak load.
1. He was glad to see 60 amp wiring. He indicated that even though the emporia is adjustable, the adjustment is in the app and too easy for the user to just dial it up. He said only for models of chargers where the current limit is set by switches or jumpers inside the box would he pass a setup with wiring rated lower than the max setting on the charger.
2. In regards to peak load, he mostly worries about things like the hot tub and air conditioning that can turn on anytime by themselves. Was not concerned about the welder and oven outlets for peak load.