He already stated that his current installation is a 60A circuit, so none of that is relevant.A lot of ideas instead of the simplest solution (short of selling it and buying a new EVSE): you can buy the J1772 head. You don't have to buy an entire cable to swap the connector.
An electrician might drop in and explain this better (or correct me) but you might encounter some mismatching issues if you swap EVSEs. Right now, your wiring was sized for 100A continuous (3 AWG) but the lugs on a 60A EVSE won't accept 3 AWG wiring (the diameter is too large), you can't terminate the wires to an outlet for 60A (has to be direct wired), and a 14-50 outlet wouldn't accept 3 AWG wiring anyway (same reason the direct wired EVSE won't accept them--they aren't expected to be connected to wiring that thick). If you look at your 100A breaker you'll probably find that the lugs are larger than a 60A breaker...unless you sized your wire and breaker for 60A, which is a different issue altogether (since the FCSP can be set up to 80A everything in the circuit should be sized for that capacity even if the installer turned the settings down).
So you might find you have to buy an 80A EVSE to replace the FCSP. Or none of this matters and the circuit is only sized for 60A in which case the FCSP should be sold because you're never going to be able to use it's full capacity.