Understood. I plan on having my electrician do a load calculation. I'm just working on a parts list for budgeting at this point. Electrical components have really increased in cost so higher amperage circuits increase the cost substantially. I was thinking that a 70-amp circuit may be most practical in my case because of wire size for 60-amp is the same 70-amp but I cant find a 70-amp disconnect so I would need to buy a 100-amp sub-panel and put a 70-amp breaker in it. If my run for the main panel to the garage wasn't 115ft it would be so bad. 2 AWG wire for a 100-amp circuit is pretty spendy.Existing unused breaker sizes mean nothing. You electrician should be able to do an NEC load calculation and determine your remaining capacity. I’d bet you can utilize the full capacity of the FCSP.