It's not a big deal. In much of the rest of the world, entire homes are on a master GFCI. Home chargers there still work fine.
 

farmtruck

Well-known member
First Name
John
Joined
Dec 26, 2023
Threads
0
Messages
85
Reaction score
113
Location
Pierre SD
Vehicles
22 F350XLT, 2 x 12 F250XLT, 23 Lightning Lariet ER
Occupation
Farmer
The breaker manufacturers are making EV specific GFCIs.
 

Mmiketa

Well-known member
Joined
Nov 25, 2023
Threads
2
Messages
165
Reaction score
247
Location
Virginia, USA
Vehicles
'23 Lightning Lariat ER
If your charger is already installed it is not required to meet the newer code, you are grandfathered in. Additionally, the 2020 NEC does not apply to every state. Virginia recently adopted it and other states have not. Some states are on 2023.
 

Sponsored

marc_hanna

Well-known member
First Name
Marc
Joined
May 16, 2024
Threads
3
Messages
151
Reaction score
121
Location
Nova Scotia
Vehicles
'23 Lightning Lariat ER; '25 Tesla Model 3; '16 Porsche Macan S; '87 MB 560SL
I do find that that the GFCI breakers are overly sensitive. I am optimistic that manufacturers will improve.
 

shelnian

Well-known member
First Name
Ian
Joined
Sep 15, 2022
Threads
0
Messages
78
Reaction score
42
Location
Seattle
Vehicles
2022 Mach-E Premium ER, 2023 Lightning XLT SR 312A
Occupation
Retired
My in-laws were experiencing GFCI breaker tripping almost every day with their ChargePoint EVSE. I hardwired it and replace the GFCI breaker with a standard one and it hasn't had a problem since.
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,653
Reaction score
4,640
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
It's not a big deal. In much of the rest of the world, entire homes are on a master GFCI. Home chargers there still work fine.
The rest of the world uses RCD (residual current detectors), not GFCIs. The RCD trip threshold is between 5 and 6 times higher than our GFCIs.
 

Ricks Lightning

Well-known member
First Name
Rick
Joined
Jun 13, 2024
Threads
8
Messages
227
Reaction score
194
Location
Los Angeles
Vehicles
2023 F150 Lightning Pro, 2024 F150 Lightning Flash
Occupation
Plumbing Contractor
I installed the 50 amp gfci spa style outdoor rated disconnect off my main panel 50 amp breaker. But since the charger is 240 volts there is no neutral wire connection from the chargers plug in 4 wire cord to the charger. So I only ran a 50' 6-2 with ground romex from the spa gfi disconnect to the non fusable disconnect inside the charger exterior lockable outdoor charger.

Just to Recap. 50 amp main breaker feeding the outdoor spa gfci disconnect 3' run ran 4-6 gauge wires 2H,1N,1G. From the spa gfci disconnect ran 50' of 6-2 Romex with ground. No neutral.
This then comes into my outdoor 24"x18" outdoor rated lockable box. Inside the box is my 50amp non fusable disconnect, fedding my nema 14-50 outlet. #6- 2H, 1G. Remember that the charger has a 14-50 4 wire cord with plug. But the neutral wire inside the charger is not connected.

So since there is no Neutral wire from gfci spa panel to the charger, I've had the gfci trip 1x when the pull out non fusable disconnect wasn't fully pushed in and got hot. Seems like these cheap disconnects are not machined perfectly to allow for easy engagement.

Without the need of a neutral, my gfci still worked fine on my 50amp charger.

Rick
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,653
Reaction score
4,640
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
I’ve talked to a guy on the code panel. He expects that a NITMAM (Notice of intent to make a motion) to be filed before the July 2025 meeting where this will be voted on by the code making panel. There’s a fair chance that this either gets nixed or at least modified before being adopted.
 
Last edited:

Sponsored

marc_hanna

Well-known member
First Name
Marc
Joined
May 16, 2024
Threads
3
Messages
151
Reaction score
121
Location
Nova Scotia
Vehicles
'23 Lightning Lariat ER; '25 Tesla Model 3; '16 Porsche Macan S; '87 MB 560SL
Seems like these cheap disconnects are not machined perfectly to allow for easy engagement.
I doubt they’re machined at all. They’re most likely stamped. There’s also a good chance that the cheap ones are from the end of the run when the punch was worn out. You end up with stamped parts that aren’t very flat.
 

Mmiketa

Well-known member
Joined
Nov 25, 2023
Threads
2
Messages
165
Reaction score
247
Location
Virginia, USA
Vehicles
'23 Lightning Lariat ER
I’ve talked to a guy on the code panel. He expects that a NITMAM (Notice of intent to make a motion) to be filed before the July 2025 meeting where this will be voted on by the code making panel. There’s a fair chance that this either gets nixed or at least modified before being adopted.
The 2020 NEC where this appears has been approved and shipped since 2020. What may be happening is your state deciding if they want to adopt the 2020 NEC?
Ford F-150 Lightning New GFCI code 1738007492850-l
 

Maquis

Well-known member
First Name
Dave
Joined
May 20, 2021
Threads
9
Messages
3,653
Reaction score
4,640
Location
Illinois
Vehicles
2021 Mach-E E4-X; 2023 Lightning Lariat ER
The 2020 NEC where this appears has been approved and shipped since 2020. What may be happening is your state deciding if they want to adopt the 2020 NEC?
1738007492850-lj.jpg
What’s being discussed here is the change proposed for 2026 that would require all branch circuits for EVSEs to be GFCI protected. 2020 did not require GFCI protection for hard wired circuits installed indoors.
 

TechnoSwiss

Member
Joined
Jan 19, 2025
Threads
0
Messages
7
Reaction score
3
Vehicles
2024 Ford F-150 Lightning Lariat Carbonized Gray Metalic
Occupation
Electrical Engineer
I've got the latest version of the Eaton 50A GFCI breaker, and I've had zero issues with my Ford mobile charger using it.