Anyone getting their EVSE installed in anticipation of their Lightning ?

Delivery tomorrow for a 48A L2 EVSE for my garage - so excited getting antsy for the SR Lightning incoming next month.

Hoping for early delivery as many FB posts showing people getting their Lighting 2-3 weeks earlier than Ford's estimate....

Got my electrician coming in next weekend to help me install the EVSE in my tiny garage.
Charging the Lightning will be just outside the garage.
My wife's PHEV charger is on a separate wall and she parks inside.

My electrician said, since my breaker panel is directly behind the garage wall that I want it installed, there is no need for a sub panel - saving me lots of money!
Just add a breaker, 2 gang outlet hardwire and voila!

Here's my UL listed EVSE for $450 - half the price of Ford's charger....

Screen Shot 2022-06-05 at 7.17.19 AM.png
Metroshot,
I had techs install a 40 amp RV hookup in my garage a couple years ago right before I got my Model 3. What that is, is the nema 14-50 outlet box on the wall. It contains a 40 amp hookup for. Mobil charger and a couple 110 outlets for plugging in other garage items when the car wasn't charging for a little more versatility.
Am gonna ask the tech to come back to see about upgrading to either a 50 amp or 100 amp subpage that can do the home backup system. That would be awesome. šŸ‘
 

gorwell

Well-known member
First Name
Andrew
Joined
Jul 19, 2021
Threads
18
Messages
819
Reaction score
1,116
Location
Sacramento
Vehicles
Ioniq 5 / XLT Standard
I have that charger.

Best bang for your buck.

I installed it with 60amp breaker. Ran 6 guage thhn to it.

Only key complaint is that the charge cord is thick.

The app is clunky, but fine as it's not something you use a lot.

Aside from the great price, I got it because of on the fly amp changes in the app.

I mostly just change at 32amp, but I like knowing I have the extra power if I forgot to start it.

Also can limit it to match my solar.
 

Tony Burgh

Well-known member
First Name
Tony
Joined
Sep 28, 2021
Threads
18
Messages
870
Reaction score
980
Location
Western Pennsylvania
Vehicles
22 Lariat ER
Occupation
Retired
Iā€™m running 6-3 from 60@ breaker through wall to 14-50 receptacle in weatherproof enclosure outside. Will use mobile charger initially. Will go to 100@ breaker, 2 gauge wire to pro charger if it ever shows up. Not very expensive when only need 6 feet of wire.
 

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
997
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
Iā€™m running 6-3 from 60@ breaker through wall to 14-50 receptacle in weatherproof enclosure outside. Will use mobile charger initially. Will go to 100@ breaker, 2 gauge wire to pro charger if it ever shows up. Not very expensive when only need 6 feet of wire.
Lucky youā€¦I have a 26ā€™ linear run of #3 Copper in conduit and the supplies are going to run me about $1,200ā€¦ouch!šŸ¤‘
 

Tomwilli2025

Well-known member
First Name
Tom
Joined
May 19, 2021
Threads
8
Messages
125
Reaction score
88
Location
Alabama
Vehicles
2022 Lightning Lariat-ER Max Tow
Occupation
Sales
Lucky youā€¦I have a 26ā€™ linear run of #3 Copper in conduit and the supplies are going to run me about $1,200ā€¦ouch!šŸ¤‘
Do you mind sharing your parts list? Where are you sourcing your wire?
I have a 120 foot linear run. I'm overthinking my options and looking solutions. I have a 200 amp service and electrical tells me I can add add another 80 amp breaker to my main. Trying to decide on which sub panel, type conduit and will probably go ahead and install a 14-50 off the new sub panel as well a junction box for the FCSP. Buy once, cry once.
Thanks.
 

Sponsored

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
997
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
Do you mind sharing your parts list? Where are you sourcing your wire?
I have a 120 foot linear run. I'm overthinking my options and looking solutions. I have a 200 amp service and electrical tells me I can add add another 80 amp breaker to my main. Trying to decide on which sub panel, type conduit and will probably go ahead and install a 14-50 off the new sub panel as well a junction box for the FCSP. Buy once, cry once.
Thanks.
Ouch 120ā€™ of Copper! I understand your pain and do feel lucky.

I wish I was that handy to have a detailed parts list to provide youā€¦I pulled that cost info from the proposal sheet from my E contractorā€™s bidā€¦he didnā€™t detail it out that deep. He wired my house when I built 14 yrs ago and provided the lowest bid, so I felt comfortable with the summary of cost & labor (3/4 day @. $750/day). The total was $1675.

When I originally built, I asked my E-contractor to wire in a 60A Critical Load sub-panel with a manual transfer switch and an external NEMA 14-50 connection for a portable generator. That left me plenty of room in my main 240V/200A service panel, so he has plenty of room to add the new 100A breaker for the new EVSE circuit to supply the 80A FCSP.

Everyone I talked to during my bid process told me their costs on conduit and Copper wire is currently insaneā€¦.and, changing sometimes daily (up). They all suggested an option to use an Aluminum conductor to defray costs, but I didnā€™t ask for pricing as there is very little detailed info available on installation of the FCSP. I was also given a suggestion to use Al for the bulk of the run, terminated in Copper, but I chose to stay all Cuā€¦ā€¦

Sorry I couldnā€™t provide more cost detailsā€¦ā€¦.
 

lancersrock

Well-known member
First Name
Kody
Joined
Aug 27, 2021
Threads
8
Messages
390
Reaction score
336
Location
USA - IA
Vehicles
2021 Honda Pilot, 2011 Mustang GT, 2013 fusion se
Occupation
Field Engineer
Funny you noticed that - $10 less for a non UL EVSE was a no brainer...
As a UL employee I greatly appreciate the fact that consumers care enough to know the difference, most people would just take the non listed one as they don't understand the difference.
 

Tomwilli2025

Well-known member
First Name
Tom
Joined
May 19, 2021
Threads
8
Messages
125
Reaction score
88
Location
Alabama
Vehicles
2022 Lightning Lariat-ER Max Tow
Occupation
Sales
Ouch 120ā€™ of Copper! I understand your pain and do feel lucky.

I wish I was that handy to have a detailed parts list to provide youā€¦I pulled that cost info from the proposal sheet from my E contractorā€™s bidā€¦he didnā€™t detail it out that deep. He wired my house when I built 14 yrs ago and provided the lowest bid, so I felt comfortable with the summary of cost & labor (3/4 day @. $750/day). The total was $1675.

When I originally built, I asked my E-contractor to wire in a 60A Critical Load sub-panel with a manual transfer switch and an external NEMA 14-50 connection for a portable generator. That left me plenty of room in my main 240V/200A service panel, so he has plenty of room to add the new 100A breaker for the new EVSE circuit to supply the 80A FCSP.

Everyone I talked to during my bid process told me their costs on conduit and Copper wire is currently insaneā€¦.and, changing sometimes daily (up). They all suggested an option to use an Aluminum conductor to defray costs, but I didnā€™t ask for pricing as there is very little detailed info available on installation of the FCSP. I was also given a suggestion to use Al for the bulk of the run, terminated in Copper, but I chose to stay all Cuā€¦ā€¦

Sorry I couldnā€™t provide more cost detailsā€¦ā€¦.
Thanks for the reply.
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
52
Messages
681
Reaction score
466
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
Lucky youā€¦I have a 26ā€™ linear run of #3 Copper in conduit and the supplies are going to run me about $1,200ā€¦ouch!šŸ¤‘
Why not #4 THHN? #3 is typically Romex witch is crazy$
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
52
Messages
681
Reaction score
466
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
Here are my conduit parts for one EVSE:

Secondary Charger
Panel
3/4" Screw Cap
3/4" Nut x 2
3/4" set screw connector
3/4" EMT 40'?
3/4" EMT Joints & straps
3/4" set screw connector
3/4" Nut
1 in. x 3/4 in. Rigid Reducing Bushing
1" LB
1" IMC (13"? two threaded male ends)
1" Nut x 2
1" Screw cap
EVSE
 

Sponsored

jefro

Well-known member
Joined
Oct 28, 2021
Threads
3
Messages
699
Reaction score
231
Location
Texas
Vehicles
F150, Corvette, Bolt EV,
I purchased my EVSE well before I bought my first EV. The one I selected has a jumper that set's maximum current so it can be used on a number of circuits.

You may find that such a high rate may be of no value. How many miles do you expect to replace each day on average?
 

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
997
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
Why not #4 THHN? #3 is typically Romex witch is crazy$
I get the cost issue, but with the FCSP max capacity to accept 80A to max its charge outputā€¦so does the cost:
  • #4 AWG has 85A ampacity but should conduct at most 68 amps.
  • #3 AWG has 100A ampacity but should conduct at most 80 amps.
https://learnmetrics.com/100-amp-wire-size/

On my cost benefit analysis, the 80A vs 60A (assuming 60A is the closest dip setting on the FCSP) supply to the FSCP going into the future is worth the cost difference in my situationā€¦..
 

PV2EV

Well-known member
Joined
Apr 17, 2022
Threads
52
Messages
681
Reaction score
466
Location
Oregon
Vehicles
2015 Chevy Volt, 2006 Kubota L39, 2006 Suzuki Eige
I get the cost issue, but with the FCSP max capacity to accept 80A to max its charge outputā€¦so does the cost:
  • #4 AWG has 85A ampacity but should conduct at most 68 amps.
  • #3 AWG has 100A ampacity but should conduct at most 80 amps.
https://learnmetrics.com/100-amp-wire-size/

On my cost benefit analysis, the 80A vs 60A (assuming 60A is the closest dip setting on the FCSP) supply to the FSCP going into the future is worth the cost difference in my situationā€¦..
Interesting website. I referenced the wire manufacturers site and got #4 @ 75C. Also I trust the electrician who wired for it at my WA home. He used #2 AL Service Entrance Cable, but would have used #4 CU if I wanted to pay for it.

If I have to go #3, I will need bigger conduit and will have to use ugly ass PVC.

Now I am triple guessing the choice:oops:
 

Firestop

Well-known member
First Name
Firestop
Joined
May 6, 2022
Threads
13
Messages
1,033
Reaction score
997
Location
Oregon
Vehicles
2022 F-150 L Lariat ER; Honda Accord Touring
Interesting website. I referenced the wire manufacturers site and got #4 @ 75C. Also I trust the electrician who wired for it at my WA home. He used #2 AL Service Entrance Cable, but would have used #4 CU if I wanted to pay for it.

If I have to go #3, I will need bigger conduit and will have to use ugly ass PVC.

Now I am triple guessing the choice:oops:
Yeah, Iā€™m trusting the advice/choices of my electricianā€¦he did me a solid when he roughed-in/finished my house when I built it and feel good about his work. On a side note, anticipating getting this truck is about as exciting as watching todayā€™s OSU v Vanderbilt Regional baseball gameā€¦changing almost every inning šŸ˜µā€šŸ’«
 

Tomwilli2025

Well-known member
First Name
Tom
Joined
May 19, 2021
Threads
8
Messages
125
Reaction score
88
Location
Alabama
Vehicles
2022 Lightning Lariat-ER Max Tow
Occupation
Sales
I have spent so many hours going through different wiring scenerios for my build and still trying to come up with best solutions. My issues is that I have a 120 foot pull with a 20 feet concrete slab in the middle. The slab has a 1.5" conduit with my fireplace starter gas line in it. So I've decide to remove that gas line. "wife doesn't know this yet". The city inspector says the conduit doesn't meet code so I have to put a piece schedule 40 or EMT in that conduit. With conduit generally being in 10 feet sections, the coupler needed to join conduit restricts me down to 1" unless I can find a 20 foot section. With 1" conduit, fill rate only allows 3 conductors of #4 and a #8 ground.

So, I'm thinking of.....
New circuit with a subpanel pulled to my garage. 125ft linear of cable. #4 2L, 1N and a #8 ground. Ran in Conduit of your choice. I will install 20ā€™ of 1ā€ EMT in the concrete slab. (Iā€™m removing the gas line) Because for the flange on Sch 40, I think EMT with a Rain Tight Coupling may be smaller overall diameter. If I could get a 20 ft section of Sch40 I wouldā€™nt have to worry about joining them or overall diameter. Let me know your thoughts on the type conduit.



125ft of #4 2L, 1N and a #8 ground

100 or 125 amp GE Sub panel

2- 80 amp GE breakers (for main panel and sub)

70 amp (for future Ford Charge Station Pro)
50 amp GFI ( for NEMA 14-50)
Industrial NEMA 14-50 receptacle ( @ 24ā€- 30ā€ from sub panel) plus box and plate

In wall junction box for future EVSE ( @ 24ā€ ā€“ 30ā€ from sub panel)

Anyone got any bright ideas..