Here you go:Will you quote the section you are referring to?
(B) Vehicle-Mounted Generators
The frame of a vehicle shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by a generator located on this vehicle under the following conditions:
The frame of the generator is bonded to the vehicle frame, and
The generator supplies only equipment located on the vehicle or cord-and-plug-connected equipment through receptacles mounted on the vehicle, or both equipment located on the vehicle and cord-and-plug-connected equipment through receptacles mounted on the vehicle or on the generator, and
The normally non-current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
The section specifies, for vehicle-mounted generators, the only accepted exceptions to grounding electrode/rod required by section 205.52. So, you need to check section 205.52 as well which basically requires a ground rod for separately derive systems. Connecting a neutral bonded truck mounted generator like Pro Power through a neutral transfer switch (i.e. separately derived system) to house wiring does not meet the required exception criteria.250.34(B) does not say that.
Check this video, specifically starting at 13:23, for further explanation.