Hmmm, I wonder if one would get a different gfci behavior if combing the two 120V outlets into 240V as shown in a different thread recentlyI use the back feed breaker with UL listed interlock kit as well. My portable generator has a bonded neutral. Always worked flawlessly. I think the difference between this and the truck, is the generator's 240v outlet is not GFCI protected, only it's 120v outlets have GFCI protection. So the bonding in the house panel does not trip anything out. The truck's pro power appears to have GFCI protection on its 240 volt outlet. So that bonded neutral in the house panel is seen as a ground fault, tripping the trucks GFCI.
As far as I can tell, a ground fault or overload on a branch circuit from my house panel will trip the breakers properly. It may not be perfectly correct by code, but best I can tell, it is just as safe for overload and fault protection.
I hope someone who knows more than me can explain better.
I am not doing that. Please see the other thread a couple weeks backI am not sure I understand the details of the described installation, but I am very concerned that an interrupted neutral condition could occur and put 240 volts into the 120-volt loads if the neutral conductors are separately switched.
Hopefully that is not the case.
Steve
If you got a 4-pole transfer switch rated for what your main panel is then yes because it would switch the neutral.Is there a solution that works with a full panel interlock breaker? These small ass "critical loads" panels seem to be way less convenient than a whole panel interlock where I can pick and choose what is critical at any time not just during the original install.
Electricity flows in the path of least resistance. Just because you don’t bring the vehicle ground to the house does not mean it isn’t grounded: you’ve still got you’re house ground and it’s bonded at the panel which is still your service entrance. A fault on the truck side would trip the gfi. A fault on the house side would go to ground.If it is not up to code, it is inherently dangerous.
The codes exist to protect from dangerous installations.
Yes, you have to treat your vehicle like a source.
In your house, the source for all the house circuits is the house panel.
The NEUTRAL from the service is grounded at the utility and has to be grounded/bonded at the panel as well, for a safe install.
In your house, the neutrals of all your house circuits are all grounded/bonded at the panel, where the service is also grounded/bonded.
In the case of using your vehicle 240v outlet in the bed as a source, it already is grounded/bonded.
If you DON"T "bring over" the ground from the lightning, then you effectively have no ground in your house system!! That is dangerous!!
Ground wires are carrying current in case something goes wrong. They're a failsafe, essentially, directing current away from the plugged-in or lighting device if a problem occurs, such a short. The neutral wire completes the circuit and allows electricity to flow.
Problems occur if you have the neutrals grounded/bonded at two places, i.e., at the truck and at the panel.
The house circuits all have their neutrals grounded at the panel unless your transfer switch switches them so they do not connect to the neutral bus bar in the panel which is where the ground connection occurs.
If your transfer switch switches the neutrals as well as the hots, which pretty much all modern transfer switches do, but not all the older ones, (but check to be sure) you will have issues.
The issues will be the GFCI in the vehicle will detect a ground fault because there will be two paths to ground resulting in current differences, and open the circuit.
According to the NEC, metal parts of service equipment shall be grounded to the earth.
In addition, the grounded (neutral) service conductor shall be grounded to the earth at service equipment. With utilities, this is for ground fault elimination and for the purpose of limiting the voltage imposed by lightning, line surges, or unintentional contact with higher voltage lines, grounding is intended to shunt potentially dangerous energy into the earth from the system.
If you're connecting your generator to an electrical panel, such as a building electrical system, you must ground your generator.
The rules permit the frame to act as the grounding point instead of the grounding electrode system. Bonding the neutral to the frame is mandatory when the generator is an independent supply. The Lighting is the supply in this case.
For vehicle mounted generators, the neutral conductor must be bonded to the generator or vehicle frames if the generator supplies equipment and receptacles affixed on the vehicle or trailer.
It is not permitted to connect the grounded conductor (bonded neutral) to the ground in both sources (generator and service panel) simultaneously, as this practice could create parallel paths for the neutral current.
As I stated it’s an interlock, not a transfer switchIf you got a 4-pole transfer switch rated for what your main panel is then yes because it would switch the neutral.
It doesn’t say that, either.I believe it has to do with bonding and grounding needs to be at the same point for separately derived systems. Since the bonding is at the truck then grounding at the main panel is likely dozens of feet away so certainly not at the same point.
Hmmm, sorry I wasn't clear. I was talking about using solar and charging the truck while grid power was out. Are you able to do that? I've always been annoyed that I can't use my solar when the power goes out.I should have no problems charging truck from solar, and also selling any excess to grid at same time. The one thing I have no solution for yet is how I could set up a way to be able to sell from truck battery to grid. But there must be some way...
I can do this, since I have previously installed battery backup.Hmmm, sorry I wasn't clear. I was talking about using solar and charging the truck while grid power was out. Are you able to do that? I've always been annoyed that I can't use my solar when the power goes out.
As someone who's read a lot of regulations (not the NEC's, though - radiation and laser safety regs), all I can say is, "How true!" Maybe someday, though, generative AI will be able to read any regulations and explain to the average Joe/Joeline what the regs mean in plain English in their particular use situation.Remember Charlie’s rule for reading the NEC:
Sorry, I get hung up doing three things at once sometimes, and my edits get garbled...my kids say I am 'long winded' also, lol.Your lengthy post kind of goes around In a circle without an actual solution. Not trying to be a dick , you know way more than me, it's just less clear now than it was before.
If it's dangerous and has no ground if you don't bring the ground from the Pro Power, and also will always trip because of the required bonding on the house panel, then what is the correct, safe way to do it?