Do NOT Plug a 48A Connector into a 50A outlet to charge your EV.

Ostrichsak

Well-known member
Joined
Sep 12, 2022
Threads
9
Messages
137
Reaction score
108
Location
Colorado, USA
Vehicles
2023 F150 Lightning Lariat
I've seen a couple of people in various threads now mention having a NEMA 14-50 outlet and plugging a 48A mobile connector into this to charge their Lightning at 48A @ 240v. Do NOT do this.

A 20% buffer of whatever the circuit is rated at needs to be left for safety. This means that since a NEMA 14-50 receptacle is 50A @ 240v you want to keep your charge rate at or below 40A. Anything above that is dangerous and is asking for trouble. Having a 50A breaker doesn't mean you can run 48A. To safely run a 48A charge you'd need a 60A circuit for the proper safety margin.

I was going to reply directly to the posts I saw but this is a fundamental tenant of EV ownership and a safety concern that needs to be seen by anyone who's newer to the concept. I think this forum will have a lot of members new to EVs so it's an important message that needs to be heard.

While we're on the subject, make sure that whomever installs your EV charger outlet does so properly. Many of the melted receptacle stories you read about are caused by a receptacle that was carelessly installed. The lugs need to be fully secured to prevent the wires from loosening over time & charge/heat cycles creating resistance that will cause excess heat.

The absolute last thing I want to read about is another "EV causing a fire" when it's super rare and almost always caused by operator error of some sort that could have been avoided.
Sponsored

 

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
79
Messages
4,989
Reaction score
6,597
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
What do you do about 14-50 outlet? A 14-60 outlet appears to have a different pin arrangement
A 60amp breaker should have a hardwired charger, not a plug-in charger. There should not be a 48amp charger with a plug.
 

PA Lightning

Well-known member
First Name
Tbone
Joined
May 27, 2021
Threads
7
Messages
426
Reaction score
542
Location
PA
Vehicles
Lightning Pro
Good posts Ostrichsak and RickLightning. Problem is with a lot of newbies to the EV world, like me, is we don't know what we don't know. I was able to get enough info from this form to get a general understanding of the different chargers and their requirements.

After reading the forum for about a year, I decided to use the Ford Mobil Charger with a NEMA 1450. The cable I had installed is 6/3 with a ground using a 50a breaker. That has working fine, but if I find I need more juice, I will have the electrician hard wire a 48a and swap the breaker to a 60a.

Keep up the good work fellows.
 
OP
OP
Ostrichsak

Ostrichsak

Well-known member
Joined
Sep 12, 2022
Threads
9
Messages
137
Reaction score
108
Location
Colorado, USA
Vehicles
2023 F150 Lightning Lariat
Good posts Ostrichsak and RickLightning. Problem is with a lot of newbies to the EV world, like me, is we don't know what we don't know. I was able to get enough info from this form to get a general understanding of the different chargers and their requirements.

After reading the forum for about a year, I decided to use the Ford Mobil Charger with a NEMA 1450. The cable I had installed is 6/3 with a ground using a 50a breaker. That has working fine, but if I find I need more juice, I will have the electrician hard wire a 48a and swap the breaker to a 60a.

Keep up the good work fellows.
Thanks. Just trying to pay it forward since I was once a n00b to all of this stuff and people provided useful info and experience at points along my journey.

Your electrician will likely have to replace the wire between the new wall connector and the breaker too. This is the part of the install that can add anywhere from hundreds of dollars to thousands depending on the length of the run and if there are any complications involved with pulling it.

You may also have considerations for your panel size and a load calc may be needed to assure that you've got the room (not necessarily physically) to add the amount of amperage draw you're considering.

Just some things to be aware of for consideration.
 

PA Lightning

Well-known member
First Name
Tbone
Joined
May 27, 2021
Threads
7
Messages
426
Reaction score
542
Location
PA
Vehicles
Lightning Pro
Thanks. Just trying to pay it forward since I was once a n00b to all of this stuff and people provided useful info and experience at points along my journey.

Your electrician will likely have to replace the wire between the new wall connector and the breaker too. This is the part of the install that can add anywhere from hundreds of dollars to thousands depending on the length of the run and if there are any complications involved with pulling it.

You may also have considerations for your panel size and a load calc may be needed to assure that you've got the room (not necessarily physically) to add the amount of amperage draw you're considering.

Just some things to be aware of for consideration.
Thanks for the heads up. I have a 400amp service to my house, so the electrician said using a 60a in one of the panels is no problem
 

Sponsored

TaxmanHog

Moderator
Moderator
First Name
Noel
Joined
Jan 19, 2022
Threads
170
Messages
12,308
Reaction score
12,957
Location
SE. Mass.
Vehicles
2022 Lightning Lariat-ER Max Tow & 2024 Harley-Davidson Road Glide CVO-ST
Occupation
Retired
Pinned thread!!
 

lancersrock

Well-known member
First Name
Kody
Joined
Aug 27, 2021
Threads
8
Messages
390
Reaction score
336
Location
USA - IA
Vehicles
2021 Honda Pilot, 2011 Mustang GT, 2013 fusion se
Occupation
Field Engineer
Thanks for the heads up. I have a 400amp service to my house, so the electrician said using a 60a in one of the panels is no problem
400!!! Here I am with what I thought was 100 amp service until the electrician told me the socket meter is actually only good for about 80 (old). Why do you have such a large incoming service?
 
OP
OP
Ostrichsak

Ostrichsak

Well-known member
Joined
Sep 12, 2022
Threads
9
Messages
137
Reaction score
108
Location
Colorado, USA
Vehicles
2023 F150 Lightning Lariat
Thanks for the heads up. I have a 400amp service to my house, so the electrician said using a 60a in one of the panels is no problem
400A service, huh? Nobody likes a braggard. :LOL:

Seriously though, we built this house about 16 years ago and it's a pretty nice place but the one thing I didn't know was to question the electrical service they were putting in. Since it's a ranch and we only finished the ground level they ran just enough to provide the bare minimum required to meet our needs (long before EVs were a consideration) which resulted in a both a 100A service and main panel. Ugh. If I wanted to put even one more 15A circuit in it would quite literally cost many thousands of dollars and lively surpassing the $10k mark, all told.

That's probably accurate as long as there's room in your panel too and not just your service. Sounds like you've got a system that was planned for expansion and, thus, far more future-proof than our current setup. Color me peanut butter and jelly.
 

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
79
Messages
4,989
Reaction score
6,597
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
Thanks for the heads up. I have a 400amp service to my house, so the electrician said using a 60a in one of the panels is no problem
Just to be clear, you need to make sure the wiring between the breaker and the charger is sized for 60amps.

I put in a 60 amp circuit. Electrician wanted to use 3 conductor wire, I made them use 4 conductor wire in case I ever want to put in an outlet instead (which would require a 50amp breaker, and downsizing to 40amps max for charging).
 

Pioneer74

Well-known member
Joined
Aug 16, 2021
Threads
32
Messages
3,485
Reaction score
6,216
Location
Dearborn
Vehicles
2022 Lightning Lariat ER - 2022 Mach-E Premium
Occupation
Electrician
Just to be clear, you need to make sure the wiring between the breaker and the charger is sized for 60amps.

I put in a 60 amp circuit. Electrician wanted to use 3 conductor wire, I made them use 4 conductor wire in case I ever want to put in an outlet instead (which would require a 50amp breaker, and downsizing to 40amps max for charging).
You used a multi-conductor cable? Is it 4 AWG?
 

Sponsored

RickLightning

Well-known member
Joined
Jan 17, 2022
Threads
79
Messages
4,989
Reaction score
6,597
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X

metroshot

Well-known member
First Name
Pat
Joined
Aug 26, 2021
Threads
97
Messages
2,127
Reaction score
1,749
Location
Montclair, CA
Vehicles
2022 Lariat F150L + 2023 MME
Occupation
Networking Tech
200A service and was very easy to hardwire dual 60A breakers for my 48A EVSE.

Over the summer, I have checked the cable temps and the 25" side gets warmer than the 1' 240V feed side.

Even charging at 110+ degree temps the charger has been able to delivery 11kW and never pulled back nor shut down.

And it's double duty charger - my wife's PHEV daily charger and my Lightning once a week charger...

Hats off to Emporia's 48A UL listed EVSE!
Ford F-150 Lightning Do NOT Plug a 48A Connector into a 50A outlet to charge your EV. IMG_9108.JPG
 

bmwhitetx

Well-known member
First Name
Bruce
Joined
May 21, 2021
Threads
39
Messages
1,557
Reaction score
2,162
Location
DFW-Texas
Vehicles
2022 F150 Lightning Lariat ER
Occupation
Retired engineer
Your electrician will likely have to replace the wire between the new wall connector and the breaker too. This is the part of the install that can add anywhere from hundreds of dollars to thousands depending on the length of the run and if there are any complications involved with pulling it.
Just to be clear, you need to make sure the wiring between the breaker and the charger is sized for 60amps.
Correct. @PA Lightning says he has #6 already. If the wire is THW, THWN , THWN-2 or THHN in conduit, then that is good for a 60A breaker. If it's Romex, aka NM-B then it is not. Romex only good for 55A. Good chart here:
https://www.cerrowire.com/products/resources/tables-calculators/ampacity-charts/
 

lancersrock

Well-known member
First Name
Kody
Joined
Aug 27, 2021
Threads
8
Messages
390
Reaction score
336
Location
USA - IA
Vehicles
2021 Honda Pilot, 2011 Mustang GT, 2013 fusion se
Occupation
Field Engineer
400A service, huh? Nobody likes a braggard. :LOL:

Seriously though, we built this house about 16 years ago and it's a pretty nice place but the one thing I didn't know was to question the electrical service they were putting in. Since it's a ranch and we only finished the ground level they ran just enough to provide the bare minimum required to meet our needs (long before EVs were a consideration) which resulted in a both a 100A service and main panel. Ugh. If I wanted to put even one more 15A circuit in it would quite literally cost many thousands of dollars and lively surpassing the $10k mark, all told.

That's probably accurate as long as there's room in your panel too and not just your service. Sounds like you've got a system that was planned for expansion and, thus, far more future-proof than our current setup. Color me peanut butter and jelly.
Hows that working with charging 2 evs? (guessing based on your sig).
 

jimfigler

Well-known member
First Name
Jim
Joined
Sep 13, 2022
Threads
33
Messages
991
Reaction score
805
Location
Orchard park, NY
Vehicles
23 Lightning Lariat ER, 21 Corvette Convertible
Just to be clear, you need to make sure the wiring between the breaker and the charger is sized for 60amps.

I put in a 60 amp circuit. Electrician wanted to use 3 conductor wire, I made them use 4 conductor wire in case I ever want to put in an outlet instead (which would require a 50amp breaker, and downsizing to 40amps max for charging).
There are a lot chargers out there that use a 6-50 plug.