I need help figuring out my home charging situation

millieraider

Member
Joined
Mar 13, 2025
Threads
2
Messages
9
Reaction score
0
Vehicles
honda accord
I'm considered getting one of these trucks and I need help figuring out my home charging situation. I have a 240v outlet in my garage thats on a 40 Amp breaker thats shared with my dryer(different outlet - same circuit). I was planning to use this for home charging but discovered the the outlet is a NEMA 10-30. How straight forward is it to update to a NEMA 14-50? Is it just plug and play like a typical 110v outlet? Can I just use an adapter? This outlet claims its rated up to 50 amps.. (pic attached)

My other option is, I have a another 40amp breaker for a 240v outlet in my kitchen thats not currently used. My stove is gas. I could potentially have a charger hard wired to this circuit. Adding a new circuit is not possible for me.

Second question, total house amps is 90 Amps. I know low, but has been sufficient for me since Heating/Water/Stove are gas. Will charging on 32amps draw to much power?

Ford F-150 Lightning I need help figuring out my home charging situation IMG_2666
Sponsored

 

flyct

Well-known member
First Name
Jerry
Joined
Sep 28, 2023
Threads
24
Messages
521
Reaction score
670
Location
South Florida
Vehicles
'24 F-450 Platinum & '234Ford Lightning Platinum & 2 Tesla Model Ys
Occupation
Blissfully Retired
You can repurpose the 40 amp unused kitchen range breaker and wire it to a 14-50 outlet. Then use a Ford mobile "charger" that has a 50 amp plug that will only draw 30 amps.

It's legal to ie a 14-50 to a 40 amp circuit since there is no 40 amp 240v outlet. Just label it as a 40 amp outlet.

I use a 14-50 outlet wired to a 40 amp circuit at the shed at my remote cabin. The breaker is wired to a 60 amp subpanel. Originally it was used to power my RV but now it is used as a backup charger for my EVs The sub panel also had 2 - 240 volt well pumps, a window AC unit and several lighting circuits.
 
OP
OP

millieraider

Member
Joined
Mar 13, 2025
Threads
2
Messages
9
Reaction score
0
Vehicles
honda accord
You can repurpose the 40 amp unused kitchen range breaker and wire it to a 14-50 outlet. Then use a Ford mobile "charger" that has a 50 amp plug that will only draw 30 amps.

It's legal to ie a 14-50 to a 40 amp circuit since there is no 40 amp 240v outlet. Just label it as a 40 amp outlet.

I use a 14-50 outlet wired to a 40 amp circuit at the shed at my remote cabin. The breaker is wired to a 60 amp subpanel. Originally it was used to power my RV but now it is used as a backup charger for my EVs The sub panel also had 2 - 240 volt well pumps, a window AC unit and several lighting circuits.
How about using the adapter on the current plug?
 

Firn

Well-known member
Joined
Aug 26, 2024
Threads
22
Messages
747
Reaction score
861
Location
USA
Vehicles
23 Pro ER
A 50a plug has to have 50a wiring and a 50a circuit behind it, unfortunately (fortunately?) you cannot just put a 50a outlet on that existing circuit.

Your best bet may be that hardwired 240v circuit but same as the dryer you cannot have both devices on it.

Trying to charge at any high rate with only 90a service will be tough. Just charging plus the HVAC fan would leave you little room for other loads, and that's assuming you have gas for heat and the water heater.

You will want to go with a hardwired charger set to a low level, possible even going with a house monitoring system to tailor charging. There are also devices that can be attached to the meter that could help in this situation.
 

RocketGhost

Well-known member
First Name
Spencer
Joined
May 22, 2024
Threads
4
Messages
243
Reaction score
279
Location
Memphis TN
Vehicles
2022 Lariat ER
If you use the receptacle on the same circuit as the dryer I would put an interlock of some sort to prevent both the dryer and charger to run at the same time. If they do it will overload the circuit. I believe there are devices specifically for this purpose.

Best would be to use the unused circuit in the kitchen.

With only 90a service, get a charger with adjustable amps and turn it down. And remember that you can't charge at an amperage more than 80% of the circuit capacity.
 

Sponsored

pullinggs

Well-known member
First Name
Dave
Joined
Nov 13, 2023
Threads
4
Messages
65
Reaction score
152
Location
Alta, CA
Vehicles
F-150 Lightning
Occupation
Retired
Like you, I have very limited power available in my panel (only about 60A).

My advice would be to hard wire a charger on your unused circuit (I use an EVSE from Emporia; there are many threads on this topic) and set the amperage to "something lower" than max. The preferences for my system are set to 24A, half of what it's rated for. That's typically plenty of power to have the truck charged and ready to go when I wake up every morning.

YMMV
 
OP
OP

millieraider

Member
Joined
Mar 13, 2025
Threads
2
Messages
9
Reaction score
0
Vehicles
honda accord
If you use the receptacle on the same circuit as the dryer I would put an interlock of some sort to prevent both the dryer and charger to run at the same time. If they do it will overload the circuit. I believe there are devices specifically for this purpose.

Best would be to use the unused circuit in the kitchen.

With only 90a service, get a charger with adjustable amps and turn it down. And remember that you can't charge at an amperage more than 80% of the circuit capacity.
Definitely do not plan on running both at the same time! My ideal scenario is to charge at 32 Amps with a mobile charger. Which is very sufficient for my driving. Now is it okay to run this with a NEMA 10-30 to NEMA 14-50 converter? OR is the swap from a NEMA 10-30 outlet to a NEMA 14-50 outlet just the change of an outlet?
 

FloridaMan655321

Well-known member
Joined
Jul 7, 2024
Threads
21
Messages
248
Reaction score
241
Location
Florida
Vehicles
1973 F100, 2024 Flash
Sounds like you have an old house, as do I. I actually utilized this to have an excuse to upgrade my panel and then add a 50amp circuit where I have a Tesla universal charger set to 40amps. I also installed an inlet so I can charge my home if there is an outage.

I know this isn't a direct answer, but just throwing it out there. I wanted to upgrade my panel anyways, and this was a good excuse, and a good excuse to install a generator inlet.
 
OP
OP

millieraider

Member
Joined
Mar 13, 2025
Threads
2
Messages
9
Reaction score
0
Vehicles
honda accord
Sounds like you have an old house, as do I. I actually utilized this to have an excuse to upgrade my panel and then add a 50amp circuit where I have a Tesla universal charger set to 40amps. I also installed an inlet so I can charge my home if there is an outage.

I know this isn't a direct answer, but just throwing it out there. I wanted to upgrade my panel anyways, and this was a good excuse, and a good excuse to install a generator inlet.
Yep built in the 60s
Sponsored

 
 







Top