I'm considered getting one of these trucks and I need help figuring out my home charging situation. I have a 240v outlet in my garage thats on a 40 Amp breaker thats shared with my dryer(different outlet - same circuit). I was planning to use this for home charging but discovered the the outlet is a NEMA 10-30. How straight forward is it to update to a NEMA 14-50? Is it just plug and play like a typical 110v outlet? Can I just use an adapter? This outlet claims its rated up to 50 amps.. (pic attached)

My other option is, I have a another 40amp breaker for a 240v outlet in my kitchen thats not currently used. My stove is gas. I could potentially have a charger hard wired to this circuit. Adding a new circuit is not possible for me.

Second question, total house amps is 90 Amps. I know low, but has been sufficient for me since Heating/Water/Stove are gas. Will charging on 32amps draw to much power?

IMG_2666.jpeg
Do you need to have the fast charging option? It takes forever to charge up to 80% but if you're not driving that much every day, you may not need the fast charge. That's what I am doing. No need to reply, just want to throw that out there.
 

topher10

Active member
Joined
Oct 25, 2024
Threads
4
Messages
33
Reaction score
6
Location
Louisiana
Vehicles
2024 Flash
I am a relatively new owner, but thought I would add my 2 cents:

1. I agree with the suggestion to hire an electrician if you have any uncertainty. I would not assume the existing wiring is correct. It seems wise to take the unneeded slot for the kitchen, put it in a new breaker, and run a new wire to an EVSE that lets you adjust the rate of charge.

2. As the poster above indicates, I would consider how much you drive a day and how much time you will need to recharge each night. If you are only driving 20-30 miles a day, you can charge nightly at relatively low kW and be fine. But if you are driving 180 miles a day and need it back to full each morning, that load might strain your system.

For my part, I purchased an Emporia EVSE and had it hard wired by an electrician with a 60 amp breaker. Even though it can charge at 48amps (11.5kw), I have it set to 40amps (9.6kw) because I usually drive less than 20 miles a day. I feel that gives the system a little headroom, and at 9.6kw I still only need a few hrs to top up the battery. I could get by with dialing it even lower, but not sure it makes a difference.
 

bmccaul

New member
First Name
Ben
Joined
Jun 28, 2023
Threads
0
Messages
1
Reaction score
0
Location
USA
Vehicles
2023 Lightning
Good ideas. Ultimately I think wiring a charger outlet from your unused kitchen circuit is the best way to go.

If you don’t want to bother with wiring or electrician, neocharge smart splitter is an option. Plugs into your dryer outlet, then charger and dryer plug into it.
It will cut power to charger if you turn on dryer, then resume charge after dryer stops.

https://getneocharge.com/products/n...Rg1lBpDT2FXHlcwBSJHIy3w1wFD7Y19Xw-Tv3kdy7djaw
 

flyct

Well-known member
First Name
Jerry
Joined
Sep 28, 2023
Threads
24
Messages
527
Reaction score
673
Location
South Florida
Vehicles
'24 F-450 Platinum & '234Ford Lightning Platinum & 2 Tesla Model Ys
Occupation
Blissfully Retired
Lots of good information here and some not so good.


1- Looking at the picture the OP posted it looks like the outlet is supplied with a 10 AWG orange Romex cable that is only good for up to 30 amps. Having that circuit protected with a 40 amp breaker is a fire hazard

2- sharing the dryer outlet with another outlet is another code violation and fire hazard.

3- having the outlet exposed without a cover plate is another safety hazard.

4- Plugging in a Ford mobile charger into a 30 amp outlet shout not be done since it draws 30-32 amps continuous. A 30 amp outlet/circuit is only rated for 24 amps continuous.

The good advice is to have an electrician recommend and implement a safe solution. If here is ample head room repurposing the unused 40 amp breaker and running adequate wire to a 14-50 outlet might be the best solution. A 40 amp circuit can legally supply 32 amps continuous .

Disclaimer: I am not an electrician but I’ve pulled multiple homeowner electrical permits and I’ve never failed an inspection.
 

B177y

Well-known member
First Name
Bill
Joined
Jul 16, 2024
Threads
5
Messages
243
Reaction score
261
Location
Northwest of Northwest WA
Website
www.ptcoffee.com
Vehicles
2024 Lightning Pro ER Max Tow
Occupation
Coffee Roasting
If your house was built in the '60s, you may have aluminum wiring on the stove and dryer circuits. The constant load of an EV charger was never a thought on any home wiring from that era.

I agree with some other posters to have a professional evaluate your situation and provide a professional opinion.
 

Sponsored

Tony Burgh

Well-known member
First Name
Tony
Joined
Sep 28, 2021
Threads
19
Messages
909
Reaction score
1,055
Location
Western Pennsylvania
Vehicles
22 Lariat ER
Occupation
Retired
Although I spent 40 years in various engineering groups for industry and felt qualified to install my 80 amp FCSP, I hired a licensed electrician for the installation. I knew exactly what he had to do and what wiring he needed. But if anything goes wrong, I have backup.

fwiw - I was a registered PE. That license gave validity to being an expert witness and verified my training and education.
 

shelnian

Well-known member
First Name
Ian
Joined
Sep 15, 2022
Threads
0
Messages
85
Reaction score
44
Location
Seattle
Vehicles
2022 Mach-E Premium ER, 2023 Lightning XLT SR 312A
Occupation
Retired
You can't just replace your 10-30 outlet with an EV rated 15-50 outlet, Hubbell, Bryant, or Levitron because they won't fit into a single gang box. Box will need to be a deep or oversized 2-gang box.

Isn't Ford now offering free charger installs? If not, maybe can buy a charger at a discount from your local electrical utility and hardwire it to your spare 40A circuit. I bought the ChargePoint Home Flex for $250 from my local utility.

Most local electrical codes require EV outlets to be protected by a GFCI breakers unless the charger is hardwired which is why hardwiring chargers is recommended. I have seen where the ChargePoint Home Flex chargers cause nuisance tripping of GFCI breakers to the point where the breaker trips almost every charge cycle. Had to hardwire it and replace the breaker with a standard one eliminate this.

No, wouldn't use an adapter because they can cause fires.

The 90A service should be fine unless you have any large loads such as AC units or a well pump.
 

Newton

Well-known member
Joined
May 27, 2021
Threads
11
Messages
421
Reaction score
569
Location
WA State
Vehicles
VW e-Golf, 2023 Lightning Lariat SR, Kia EV6, Toyota T-100
With an old house I would definitely keep the amperage down, you will do fine with a 32A EVSE or less. Old breakers are old and the continuous load of an EVSE will be something that your house has not encountered before.

The safest would be to hardwire a 20A/240V EVSE to the kitchen, you will find that in real life it will recharge fast enough - about 9 or 10 miles an hour. Of course people can (and will) come up with scenarios where that is not fast enough but for the odd occasion you can hit a fast charger if absolutely necessary.
 

Newton

Well-known member
Joined
May 27, 2021
Threads
11
Messages
421
Reaction score
569
Location
WA State
Vehicles
VW e-Golf, 2023 Lightning Lariat SR, Kia EV6, Toyota T-100
You can repurpose the 40 amp unused kitchen range breaker and wire it to a 14-50 outlet. Then use a Ford mobile "charger" that has a 50 amp plug that will only draw 30 amps.

It's legal to ie a 14-50 to a 40 amp circuit since there is no 40 amp 240v outlet. Just label it as a 40 amp outlet.

I use a 14-50 outlet wired to a 40 amp circuit at the shed at my remote cabin. The breaker is wired to a 60 amp subpanel. Originally it was used to power my RV but now it is used as a backup charger for my EVs The sub panel also had 2 - 240 volt well pumps, a window AC unit and several lighting circuits.
No. The only semi-acceptable way to do this is to get an adapter to convert the 14-50 male end on the Ford EVSE to work with a 40A outlet (no less!) and preferably tape it on so that it can’t be removed and used for something else. Changing the outlet to handle a connection over the wire rating is a sure recipe for disaster in the future - especially in an old house with old wiring!
 

flyct

Well-known member
First Name
Jerry
Joined
Sep 28, 2023
Threads
24
Messages
527
Reaction score
673
Location
South Florida
Vehicles
'24 F-450 Platinum & '234Ford Lightning Platinum & 2 Tesla Model Ys
Occupation
Blissfully Retired
No. The only semi-acceptable way to do this is to get an adapter to convert the 14-50 male end on the Ford EVSE and preferably tape it on so that it can’t be removed and used for something else. Changing the outlet to handle a connection over the wire rating is a sure recipe for disaster in the future - especially in an old house with old wiring!
Agreed. If you were replying to me perhaps I was unclear in my posting. The breaker should NEVER EXCEED the Wire and outlet rating.

Since there is no 40 amp 240v outlet, it is legal, customary and acceptable to use a 14-50R outlet wired for 40 amps, and protected with a 40 amp breaker. It’s done all the time with electric ranges.

My detached shed Sub-panel has a 60 amp main. Per code, a main is required in the sub-panel because it is in a detached building and has more than 6 breaker handles.

It’s fed 6 AWG THHN in conduit from the house panel. The 14-50 outlet in question is wired to a 40 amp breaker in that sub-panel, using 6 AWG THHN in flex conduit.

Even though it’s labeled “car charger”, It primarily powers my RV ,so that’s why the 40 amp breaker is a standard Double Pole breaker rather than an expensive GFCI. On very rare occasions is it used as a backup EV charger outlet, since I also have a hard wired Tesla Wall Connector installed at the house which we use for the EVs.